Hi everyone, I am currently making recessed (niche) shelving and wanted to add some lighting coming from the existing switch. I want to change to switch to a 2 gang do that these light can be controlled independently from the main light. How would I go about wiring this up? I am pretty okay when it comes to stuff like this, I've added extra sockets etc. but I can't get my head around how the lighting wiring works ? any help is greatly appreciated and I can send any photos required to help out.

Thanks a lot!

20210709_204058.jpg
 
If theres a neutral at the light switch you can loop the line in the switch to the second gang and join in the neutral and cpc. If there is not a neutral at the switch you'll need to get it there from the light
 
Yes it is rcd protected. Are there any other wires tucked in the back box of the light switch.
 
No you have no neutral but as @suffolkspark suggests you maybe able to repurpose the cut off red but your picture of the light fitting itself is worrying. There used to be a ceiling rose there but the new fitting only has a single flex up into the ceiling cavity and what looks like a DIY job it is highly likely that flex is connected to unenclosed block connectors. It may be time to get an electrician in.
 
You have a 2-way switching arrangement here (should be another switch that controls the same light). There may, or may not, be a permanent live at the switch, and if there is one, it could be any one of the 3 reds. Looks like there's a hidden junction somewhere too, complicating things. This is probably beyond DIY, best get a professional in for this one.
 
Theres Junction box joining cables somewhere then, youll likely need to get access from above to see whats going on
I will be changing all floors upstairs so I'll have a look then at what's going on. I'll leave some lighting cable at the neiche boxes and once the floor is lifted and I can figure out what's going on it should be easier to wire it all up or I'll get an electrical in. Thanks for your help!!
 
No you have no neutral but as @suffolkspark suggests you maybe able to repurpose the cut off red but your picture of the light fitting itself is worrying. There used to be a ceiling rose there but the new fitting only has a single flex up into the ceiling cavity and what looks like a DIY job it is highly likely that flex is connected to unenclosed block connectors. It may be time to get an electrician in.
It seems like I right mess ? as I said to @suffolkspark I'll leave some wire at the neiche boxes and once I'm doing the upstairs floors I'll have a look at what's going on and if I manage to fix it at least the cables are there to connect it all up or get a professional out to do it. Thanks for your help!
 
You have a 2-way switching arrangement here (should be another switch that controls the same light). There may, or may not, be a permanent live at the switch, and if there is one, it could be any one of the 3 reds. Looks like there's a hidden junction somewhere too, complicating things. This is probably beyond DIY, best get a professional in for this one.

I can't seem to see another switch, could have been one somewhere before but I'm not sure. Going to leave it for the meantime and have a look at what's going on in the ceiling cavity at a later date. It's getting a bit too much for my knowledge and skill. Thanks for your help!
 

Reply to Adding lights and a 2 gang switch in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
591
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
616
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
1K
I genuinely can't find a 3 gang 3 way black smart light switch - any ideas where I can get one from? Seems to be hard to get hold of?
Replies
4
Views
666
My kitchen had an extension at some point and the 2 lights are switched from a 2 gang light switch. It's separate circuits so I can't join them...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock