In theory you could add RCD sockets if the cable doesn't need RCD protection but the chances of that being the best option are pretty slim.
 
In theory you could add RCD sockets if the cable doesn't need RCD protection but the chances of that being the best option are pretty slim.
Not if the socket you are spurring from is already a spur and there isn't an FCU involved
 
Rcd spurs are not recognised by BS7671 as a means of providing additional 30ma rcd protection so it would have to be listed as a departure.
 
Rcd spurs are not recognised by BS7671 as a means of providing additional 30ma rcd protection so it would have to be listed as a departure.
... that's still OK though isn't it? As you say, if it's listed as a departure. As long as the cable installation method does not require RCD protection presumably? Does an RCD spur protect the load side or supply?
 
Your departure would have to have the same level or better than suggested by BS7671, not something I would be trying to prove.
 
Your departure would have to have the same level or better than suggested by BS7671, not something I would be trying to prove.
I'm sure I read an article somewhere where at least one of the schemes decided that it was an oversight when writing the list of devices and that all things considered they were acceptable.

However I'm not sure ' I think I read it on the internet somewhere.' would be a valid defence. :D
 
Read and understand APPN15 EVEN THE VAULTED SCHEMES have to apply 7671 to their acceptance procedure. Apart from the obligatory numerous pound notes, and hoops you have to jump through you need to join every 12 months, just to keep parasites in beer money. Going to get deleted isn't it?
 
Read and understand APPN15 EVEN THE VAULTED SCHEMES have to apply 7671 to their acceptance procedure. Apart from the obligatory numerous pound notes, and hoops you have to jump through you need to join every 12 months, just to keep parasites in beer money. Going to get deleted isn't it?
Appendix 15 makes no reference to additional rcd protection so maybe you should read it.
 

Reply to Adding socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
619
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
258
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
932
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
1K
Hi, my friend is having a floating shelf with a electric fire, and I’m between minds where to put the socket, I was gonna put the socket behind...
Replies
3
Views
548

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock