I want to add 2 double sockets to what is either an existing spur or the end of a radial circuit (there are only 3 wires) I cannot trace the cable back so I've no idea how it is wired at present. If I fit an FSU immediately after the existing socket will this then allow me to add the extra sockets? If I have a washing machine, spin dryer and deep fat fryer plugged into the new sockets will this cause a potential problem if they are all on at the same time, they are
 
My first plan would be size of those 3 cables, and the protection device for them. If they are 2.5mm say and the protection device is 32amps, then there is a great chance it is already a spur of a RFC, and as per appendix 15 you can only really have one single/double socket un-fused spur at each point of the ring.

If this is the case then you can be putting a serious load on that 2.5mm cable, even if your fusing your part down to 13amps, we all know that a 13 amp cartridge fuse will quite happily run for over an hour at 2 times it's rating, and then you got the whatever can be plugged into that first socket.

For me you need to know exactly what situation you have there, and you need to design your work accordingly, you can't really design something on a maybe. So if it is a unfused spur on a 2.5mm cable off a RFC, then no I would not advocate what you propose.
 
Last edited:
So if you assume it is un-fused spur could you then replace the existing socket with an FCU, add a new socket beside it then extend to the additional sockets.
That way you just have one fused spur, albeit with a limit of 13A on the all the sockets.

It does all assume though that all the appliances are ok with a limit of 13A (ish) and that it is really is a single socket on a un-fused spur to start with.

Do you also need to consider RCD protection?
 
So if you assume it is un-fused spur could you then replace the existing socket with an FCU, add a new socket beside it then extend to the additional sockets.
That way you just have one fused spur, albeit with a limit of 13A on the all the sockets.Yes that is a way of doing it, but spurs in kitchens are really IMO not a good design. About the only place in a modern home you get any type of loading on sockets is in a kitchen, and so having 3/4 double sockets backed by a 13amp fuse is not what I consider a good design. 3/4 sockets on a fused spur in a living room or the like is more acceptable.

It does all assume though that all the appliances are ok with a limit of 13A (ish) and that it is really is a single socket on a un-fused spur to start with.

Do you also need to consider RCD protection? Almost certainly the additional work will need to have RCD protection. whether the OP decides to just RCD protect his work, or the whole circuit is agian his call. I would be trying to protect the whole circuit, could never see the point of have a socket RCD protected and 2 feet away one that wasn't.

...........................
 

Reply to Adding sockets to an existing spur in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
816
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
639
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
385
I’ve had a disagreement with one of the Engineers in work. So we are doing an install. Installing an Intruder Alarm. Rather than go with my...
Replies
48
Views
5K
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock