I am doing the electrics for an extension, part of which is to add a wet underfloor heating system.

The current heating is s-plan, the boiler has a pump overrun.

The plumber has put in a 2port valve and pump which feeds one zone on the UFH with a remote programmable theromstat.

The difficulty I am having is getting the boiler to fire when the UFH calls for heat without sending power to the existing pump (this is from dagrams, its not wired yet). The boiler has L and N, the call for the boiler to fire going into the boiler and the existing pump power is from the boiler.

Anyone any ideas?
 
Its not me its because the plumber didnt want to run his pipes into the existing cupboard the lazy b.

Gonna have a think about using a relay and will get back, probably with another question
 
I dont want the existing pump the run when the underfloor heating is on, because there will be times when the Ch and HW is off. Then the pump is pumping with nowhere to go. Ive not done much on CH systems- i think it called the boiler interlock
 
you need two relays for the boiler enable, then the new UFH & pump can be on the S/L from the UFH stat and do the same for the CH & HW, this way there wont be any back feed.

To better explain: 2 relays are used to activate the boiler. On relay 1 wire the Oranges from the H/W & CH (including the pump) to A1 and do the same with relay 2 putting the new UFH valve orange and pump on to A1 - this will keep them split.
 
Last edited:
This makes sense, a couple of contactors. So when the existing system calls for boiler on, only the existing pump comes on, when the UFH calls for heat, its pump comes on.

Makes sense now, thanks

No thanks button on the screen or I would thanks you both!
 
Last edited:
you need two relays for the boiler enable, then the new UFH & pump can be on the S/L from the UFH stat and do the same for the CH & HW, this way there wont be any back feed.

To better explain: 2 relays are used to activate the boiler. On relay 1 wire the Oranges from the H/W & CH (including the pump) to A1 and do the same with relay 2 putting the new UFH valve orange and pump on to A1 - this will keep them split.

That'll kill the boiler in a few months, hope his insurance is up to date!

Overrun boilers must have a pump connected to the pump overrun terminal.
 
Like this but the original pump will be connected to the pump live terminal in boiler, oranges connected to switch live in boiler and boiler permanent live connected with the greys of the valves.
 

Attachments

  • image.jpg
    127 KB · Views: 97
It's very unusual to run the underfloor pump without the circulating pump, but then I haven't seen the pipework to know what's going on.
To achieve seperate pumps will require two relays connected so that they each connected run their respective pumps when the call signal is live from the valves but also the normal circulating pump must default to being connected to the boiler pump terminal.

The normal setup is that the underfloor pump only circulates water through the underfloor heating after the blending valve, with the normal circulating pump effectively delivering the hot water to the underfloor system. To do this you can use just one relay to operate the boiler fire from the underfloor valve
 

Reply to Adding underfloor heating to a s-plan system in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
904
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
At the moment it depends on the weather on how well the central heating works, the main problem is the Nest Gen 3 thermostat only measures the...
Replies
7
Views
641

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock