As you know I have been out of the "game" for a while so not up to speed with current regs, work practices, testing etc etc as the last test I did was clipping the leads to the apprentices ears and winding up the Megger, I can't remember the reading as the screaming made me loose concentration :D
Anyways,
My architect based down in Limehouse renting work space in a building bought himself a CNC machine and off course when he powers it up it trips the RCCB so I am looking to get some advice from the knowledgeable sparks on here so that I can pass the advice on to save him being ripped off.
Below I have pasted in a photo of his board as well as the label off the motor on the CNC machine (its not 3 phase BTW) he also tested the machine out in one oh hie "neighbours" work spaces and it works fine and nothing trips but as you will see from the photo the install is criminal and I have never seen a bodge like it.
Any help appreciated.
could the 300Hz be the cause of the RCD tripping? motor incompatible with RCD.
How is he connecting this machine.
He said with a 3 pin plug on the end of the lead, but it works in one work unit fine but not in his, spec on the motor in the link shows 220 or 380, so the plate says 1.1kW so it looks like its the 4147-A motor as listed below due to the RPM.
I'm no expert on motors but surely the 300Hz motor isn't designed for direct connectionn to 50Hz supply?
If he is plugging this to a 13A socket I can only assume the machine has a phase / frequency converter fitted which is an expensive bit of kit. This may also offer variable speed drive of the motor by changing the frequency. I wouldn't mind seeing the inside of the control enclosure. According the motor plate it is only a year old and maybe he should refer to the manufacturer with regards to the rcd tripping.
The thing is when its plugged in to a standard socket elsewhere (the one with the dodgy CSU) it works fine, I am trying to get some more info as we speak.
On the second board is the mcb for the circuit he is plugging in to defititely rcd protected?
I would suggest the 3phase motor is powered by a 1ph to 3ph VSD, the drive output been 300hz to generate the high speed tabulated on the motor. The motor seems to be designed for this going by the plate, as for the tripping, well the drive will probably be sending designed earth leakage in excess of the RCCB rating or taking it passed its limit if existing earth leakage exists from other circuits, was the other installation it was plugged into RCD covered?
Anyways,
The implication being that if he calls someone the inevitable outcome is he'll be ripped off?
Sorry but I find that implication quite offensive on a public forum.
What is Joe Public viewing this post and considering getting an electrician in going to make of that?
Reply to Advice Needed - CNC Machine Tripping in the UK Electrical Forum area at ElectriciansForums.net
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...