TN-S. Domestic 1.5 kW shower on a 6mm2 T&E clipped direct for the most part and in some plastic trunking for about 200 cm Total cct length is about 15M. The manufacturers label inside the shower itself states that it is a 9.6kW shower at 230V - should i take this as the power rating or the one also stated as 10.5kW at 240V (now we operate to 230V maybe i should take this as the power rating?) But I refer here to the 10.5kW rating.

Trips out a 32A MCB no problem (DIY installed shower and shower upgraded from previous). Told the customer i've got to include 30mA RCD and increase the MCB size. From what i can work out, the maximum i can go to will be at 46A. I would rather use a lower size cct protection at 40A, but am i likely to find this will trip out with the power rating here.

How much of an issue is the 200cm of cable enclosed in the plastc mini trunking, will this significantly decrease the current rating in this case, or at this length not an problem?

The customer is going to have the hump when i tell him i've got to put Main Bonding in as none present, not keen on swaping out the shower for a less powerful one. Changing the T&E from 6mm2 to 10mm2 is the obvious solution, but wanted to double check the MCB situation - would i be risking it using a 45A MCB on a cct when the regs say 46A is the maximum this cct design can take?
 
Last edited by a moderator:
OP
1

1shortcircuit

How long is a shower on for?

How long is a cable tested for to prove rating of cable?

Go through your cable calcs applying the correct factors and PROVE wether a 45A mcb will be adequate:thumbsup


Hang on a minute, you're just wanting to cheat the system and get a quick answer aren't you ;)

Stop being lazy lol
 

kingeri

Electrician's Arms
Messages
2,604
Location
Yorkshire
The section of cable in the mini trunking should technically be de-rated, don't have my books handy so can't be more specific, sorry. And doesn't matter what he says about main bonding, if he won't let you do that then just walk away!
 

darkwood

Super Moderator
Staff member
Super Moderator
Moderator
Mentor
Electrician's Arms
Trainee Access
Messages
13,285
Location
West Yorkshire
Measure the supply voltage, if its 230v use the 230v rating if its as i suspect 240v or their abouts use that rating. Yes agree we use on paper 230v now but rarely come across this in domestic.
 
OP
K

Knobhead

Measure the supply voltage, if its 230v use the 230v rating if its as i suspect 240v or their abouts use that rating. Yes agree we use on paper 230v now but rarely come across this in domestic.
The resistance of 9.5KW @230V is 5.568 Ώ giving a current of 41.3A.
@240V the current through 5.568 Ώ becomes 43.1A giving an output of 10.34KW
 

Richard Burns

Respected Member
Mentor
Electrician's Arms
Trainee Access
Messages
9,926
Location
Cambridgeshire
You have current of about 42A with either value of power as they are almost the same within a fraction.
If you have 6mm T&E in trunking this is a CCC of about 36A so this would not meet the regs. The clipped direct would meet the regs at 46A.
You could use 40A RCBO as protection since it is on for only a few minutes, but you would need to justify the CCC for trunking run; is it horizontal or vertical is it buried in insulation, is there clear air flow through the trunking or is it sealed at either end.
 

Guitarist

Regular EF Member
Messages
5,250
Location
Norfolk
Very rarely is cable clipped direct along its whole length for a shower. Most of the time it will be run through conduit inside the wall, or pass through insulation in a loft.
I can't believe we are doing the whole shower thing again! :)
 
OP
F

freedomrun

This install is in a GFF. Cable runs under the floorboards and then up a wall in mini trunking - is a value stated anywhere for the minimum legnth of cable permitted in trunking BEFORE de-rating has to be calclated?

I'm only asking for some advice here, not for calculations to be performed for me - I'm not lazy. Thanks.
 
OP
D

drew35

If he doesn't want bonding ask him if he ever wants to be found lying dead and naked in the shower, after electrocution, and in a pool of his own pee n' poo? Ambulance staff pointing and laughing at his tiny pee pee!

Basically how I'm found after each and every Birthday party, apart from the dead part, and only occupationally electrocuted!
 
OP
F

freedomrun

The bonding is not a problem - he has it installed or i'm not doing the work, that's it. My question is about the overcurrent protection at the top end of stated reg limit.
 

Richard Burns

Respected Member
Mentor
Electrician's Arms
Trainee Access
Messages
9,926
Location
Cambridgeshire
Under the floor boards is reference method B as well, not reference method C, so it looks like you are running a cable with too low a CCC for the applied load!
 
OP
F

freedomrun

True. I have no access to the cable installed under the floor, so i should assume worst case install method for T&E within reason - would'nt of thought insulation would be present in a ground floor flat and it's an old Victorian property converted years ago.
 
OP
F

freedomrun

Well, my original thoughts on this were that Ref C was the one to go for.
 
OP
S

SirKit Breaker

The shower is irrelevant in this calculation. You need to spec your protective device for the rating of the cable, not the rating of the appliance. If the appliance needs more power than the cable can supply, then the cable needs to be upgraded to allow higher rated breaker to be fitted. This must of course be done with consideration to correction factors, volt drop and so on.

Cheers...........Howard
 

darkwood

Super Moderator
Staff member
Super Moderator
Moderator
Mentor
Electrician's Arms
Trainee Access
Messages
13,285
Location
West Yorkshire
The resistance of 9.5KW @230V is 5.568 Ώ giving a current of 41.3A.
@240V the current through 5.568 Ώ becomes 43.1A giving an output of 10.34KW
Not sure why you given me this info the OP has already expressed the shower has a duel rating lable of both 230v and its equiv' at 240v, i wasn't in any doubt that the element resistance remains constant while the ampage increases with voltage increase or vice versa. I mearly asked him to measure the voltage to guide him to which one to work his calcs to.
 

Richard Burns

Respected Member
Mentor
Electrician's Arms
Trainee Access
Messages
9,926
Location
Cambridgeshire
why? under floor is either clipped direct od in free air.
From BS7671 installation method numbers 40 or 47 seem to apply here, either in a building void or in a suspended floor, unless the space is deeper than about 200 or 600mm respectively, which could be the case but is probably unlikely. Both of these are method B.
Looking at the intent of the installation methods, if a cable is in an enclosed space without being in close contact with a conductive surface this is method B.
Alternatively if the cables were stretched across and did not reach the floor then you maybe able to call it free air, but an unlikely installation method (perhaps!)
I would tend to be erring on the side of B.
 
OP
G

Geoffsd

Either way, it doesn't matter.

Both ratings are over 40A - so too high for 40A mcb and too high for 6mm² in conduit.

Smaller shower or lots of work.
 

valleybilly

Scuber Do
Messages
218
Location
Manchester
Best practice rules here , Dont take crap off customers who winge at the cost as its your ass next if all goes wrong . Hes employing you to do it right not DIY it as before , If he dosent like whats best then walk ! , Its suprising how good it feels & i bet he calls you back .
 

somersetsparks

Regular EF Member
Messages
1,251
in your average gaff, under the floor is reference method B, according to my tables, I seem to remember at college it has something to do with air movement or lack of it
 
OP
F

freedomrun

I'll use Ref B then - what would be the minimum permitted length of cable within trunking before factors need to be applied?
 

Richard Burns

Respected Member
Mentor
Electrician's Arms
Trainee Access
Messages
9,926
Location
Cambridgeshire
Let’s summarise here
All this is only considering the installation method, the regulations, my thoughts.
This does not consider volt drop or any other applicable derating factors.

Cable run 15m of 6mm[SUP]2[/SUP] T&E all installed to reference method B (in my opinion)
Shower 9.6kW @ 230V or 10.5kW @ 240V
Protection device not yet selected.

CCC for 6mm[SUP]2[/SUP] multicore 70[SUP]o[/SUP]C
Ref B 38A
Ref C 46A

Current demand of an instantaneous water heater (no diversity permitted)
9.6kW @ 230V I=P/V = 41.7A
10.5kW @ 240V I=P/V = 43.75A

So in order to carry a current of maximum 43.75A then a 6mm[SUP]2[/SUP] cable must be installed to reference method C and cannot be installed to reference method B.

Questions you have:

Can I use a 45A MCB?

For the shower as an appliance and if the cable were suitable – Yes
For 6mm[SUP]2[/SUP] T&E installed to Ref method B – No (also you cannot use a 40A MCB)
For 6mm[SUP]2[/SUP] T&E installed to Ref method C – Yes

What is the maximum length of trunking before derating is required?

The regulations do not state a minimum length before derating is applied.
You could possibly consider as an electrician that the regulations do give variable derating factors for different lengths of cable in insulation. If you were to apply the same considerations to trunking this would mean that full derating is applied if the length is greater than 50cm. As your length is 200cm full derating would apply.

Solutions available:
Use the 6mm[SUP]2[/SUP] cable as a pulling wire to draw 10mm[SUP]2[/SUP] cable in to replace it, use a 45A MCB, upgrade bonding.

Decide that under the floor is reference method C, remove the trunking, use the existing cable, use a 45A MCB, upgrade bonding.

Read the manufacturers instructions and decide if they specify that you can use any other method of safe installation as these would override the wiring regulations.
 
OP
F

freedomrun

Replacing the Shower would be my pref choice - customer not having it, but all i can do is state all the possible options I have available.
 
OP
F

freedomrun

Richard Burns - Thankyou for taking the time out to give such a detailed asnswer. Much appreciated.
 
Status
Not open for further replies.

Permanent unswitched live colour?

  • Brown

    Votes: 99 72.3%
  • Black

    Votes: 38 27.7%

Electrician Talk

Top