I’ll Hi I need a bit of advice on our 5 year test the company has put a limitation on checking main fuses and bussbar testing due to the gas meter adjacent in the room !!
5 years previous this was not picked up is this acceptable or should they do this !
Many thanks for your help

Also they have put all socket outlets as a C2 when the installation was done at least 20 years ago should they not be a C3 as I thought you tested it as to installation and if there is a regulation that states this could someone tell me it please
 
I’ll Hi I need a bit of advice on our 5 year test the company has put a limitation on checking main fuses and bussbar testing due to the gas meter adjacent in the room !!
5 years previous this was not picked up is this acceptable or should they do this !
Many thanks for your help

Also they have put all socket outlets as a C2 when the installation was done at least 20 years ago should they not be a C3 as I thought you tested it as to installation and if there is a regulation that states this could someone tell me it please
 

Attachments

  • BestPracticeGuide4-Issue3 EICR.pdf
    1.8 MB · Views: 17
I’ll Hi I need a bit of advice on our 5 year test the company has put a limitation on checking main fuses and bussbar testing due to the gas meter adjacent in the room !!
5 years previous this was not picked up is this acceptable or should they do this !
Many thanks for your help

Also they have put all socket outlets as a C2 when the installation was done at least 20 years ago should they not be a C3 as I thought you tested it as to installation and if there is a regulation that states this could someone tell me it please
sockets without RCD protection would be a C3 normally, but if they are likely to be used to power appliances/tools outdoors, then a C2 is appropriate.
 
hi , in most domestic houses the gas meter is under the stairs next to the main head/ meter and dis board , is it different in a commercial setting ? (i am now going to check under my stairs to if i am talking rubbish lol)
 

Reply to Advice on5 year periodic test on hotels in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock