Hi All

Was wondering if anybody can help me out...

I am trying to replace a standard Honeywell thermostat with a Sunvic Programmable Room Thermostat http://www.sunvic.co.uk/tlx6501.htm

My current Honeywell thermostat (not programmable) has 4 wires coming from it

* Earth
* Neutral
* Live
* Additional - this i have been told is a link (smaller red wire)

The new Sunvic programmable thermostat only has 3 places for wires to go in the following points

* NO
* COM
* NC

Please can someone tell me what goes where as I am confused?

Thanks in advance
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
Welcome to the forum matey, I don't have that kind of knowledge to answer that question, but I'm sure someone on here will shortly
 
G

Grae79

  • Thread Starter Thread Starter
  • #3
what do you mean a "smaller red wire"?? you mean it's shorter than the others or smaller in diameter? is it not just 3 core & E?? earth, brown (red), black (yellow), grey (blue)??
 

Dan

Admin
Welcome to the forum. :) Be sure to follow all the regs! I'm not a sparky so I'll stay out of this one.
 
D

dipsb_13

  • Thread Starter Thread Starter
  • #5
Hi All

Grae79 thanks for your response, I have attached the photo below of the wiring going to my current Honeywell room thermostat.

This is the programmabvle theremostat I have got Sunvic Controls Limited

Really appreciate your help.
 

Attachments

G

Grae79

  • Thread Starter Thread Starter
  • #6
first thing's first, make sure the exisiting stat's properly isolated before you start!! if you don't know how to do this then call in a professional, pls!!

if there's no earth on the new stat then terminate it in a conn. block...same with the neutral (blue)...seperate conn. blocks, obviously. then you want your permanent live (red) to the COM on new stat..and your switched live (yellow w. red sleeve) to N/O on the new stat. that should be that. :)
 
Last edited by a moderator:
D

dipsb_13

  • Thread Starter Thread Starter
  • #7
FANTASTIC thanks!!

Do you know where the shorter red wire would go? - the one thats going to point '1' in the image on the previous message.

Thanks again
 
D

dipsb_13

  • Thread Starter Thread Starter
  • #9
sorry i misread before

thanks very much for your help
 

Reply to Advice please: Programmable Room Thermostat in the The Welcome Forum area at ElectriciansForums.net