Discuss Air conditioning unit in the UK Electrical Forum area at ElectriciansForums.net
Im putting a new circuit in tomorrow for an air conditioning unit (im just doing the supply side). Am I right in thinking a standard 30ma rcd and b type breakers can’t be used with air conditioning units?
Tia
Tia
Depends on the size and voltage of the A/C unit Elliott 96, length of run, type of installation method, etc etc too many imponderables to make a snap decision like that.
I presume an air con company is doing the install.
ask the people supplying and installing it what spec they want for the supply.
if at all possible get them to email the spec to you.
that way if its wrong, you can divert the blame and cost back to them.
Tia
Think inrush on start up, many time during the working day?
I have had similar issues with compressors where the customer just asks for a 32A isolator fitting.
then calls back urgently to say the compressor guy is here and says the supply isn't big enough etc.
Hi Elliott
RCD would not be a requirement of the unit and you can avoid the additional protection requirement by your install method.
Type B is not recommended due to the inductive load of the compressor in condensor unit. They are almost all inverter driven now though so inrush is not generally an issue. C type is more suited to this type of load however and you should design to this.
near the bottom of the page.
suggested fuse 25A
if it were me I think 25A C type is what id be putting in.
  • CU-5Z90TBE_1,Specification_Sheet.pdf
Surely its better to have it on a rcd than not? I was going to install a sub db anyway as theres no spare ways so can install a main switch and chuck the rcd
a RCD is basically to protect persons from inadvertent contact with live parts. what is the chance of this happening in this situation?
Going to use 10mm twin and earth inside the house and then armoured on the outside
just the supply!
Why 10mm2, what do your cable calculations tell you? have you done any? What are your plans for isolation purposes? Why the cable type change?
Reply to Air conditioning unit in the UK Electrical Forum area at ElectriciansForums.net
I have a large gym in the garden and it gets ridiculously hot in the summer. I have utilised pretty much every inch of space and do not want to...
Electrical2Go - Beginners Guide to Positive Input Ventilation (PIV) Units: A Solution to Indoor Air Quality Woes A guide to Positive Input...
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
