a RCD is basically to protect persons from inadvertent contact with live parts. what is the chance of this happening in this situation?

I actually have some experience with this.
totally unrelated job to put some cat 5 cable in above a ceiling grid.
put steps up, removed tile and poked head up for a look at what I'm dealing with.

my arm brushed against a piece of copper pipe and gave me a shock. not a belter but enough to make me flinch.

got tester out, 90v between earthed grid and this pipe,

traced it back to an air con unit outside, the incoming supply to outside isolator had been connected correctly but the outgoing side to the compressor had the earth connected to an empty terminal in the rotary isolator. so no earth to the unit.
 
I actually have some experience with this.
totally unrelated job to put some cat 5 cable in above a ceiling grid.
put steps up, removed tile and poked head up for a look at what I'm dealing with.

my arm brushed against a piece of copper pipe and gave me a shock. not a belter but enough to make me flinch.

got tester out, 90v between earthed grid and this pipe,

traced it back to an air con unit outside, the incoming supply to outside isolator had been connected correctly but the outgoing side to the compressor had the earth connected to an empty terminal in the rotary isolator. so no earth to the unit.
Now you have inadvertently answered one of my questions to the OP.
 
I was going to use 70mm but haven't got enough space in the van for the drum so gonna go 10

or possibley
If your circuit is getting on for 100m and using a 32A device 10mm is of inadequate csa for vd requirements.

its actually less than 25A according to spec sheet. 10 is ok in my opinion for vd.
p.s. calcs done for swa
 
Several posts have been deleted. If you have nothing sensible to add leave the thread alone.
 
10mm too small vd wise. I think I'd be going swa all the way, too.

May I suggest to the OP that they do the calcs for what they intend to install and come back to us for a double check?

I know I've taken the mic a little bit and that has been deleted.
slap on wrist accepted.

but only the OP knows the installation methods and can judge what is best practice.

perhaps, if the OP posted the installation method, overload device and expected current it would be good to see some of the trainees use it as a real world practice.?
 
Noticed that this model of a/c is silent on running current max.
If it helps with your calcs, a similar a/c unit fused at 25A and 10kw output states a max running current of 20.6 amps. From experience the running current is much less as in our climate the fan(s) very rarely run flat out. Startup current is less of an issue , will be around 12 amps.
I fit a/c and if i was running a supply 100M i would be getting the books out on this one... lol
Good luck,
 

Reply to Air conditioning unit in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock