How do you record the details on the schedule of test results when two different cable types have been used for the supply to the outdoor unit and then the interconnecting cable?If I'm installing the whole system I will issue an EIC with the Zs taken from the furthest point (usually the indoor unit on a split).
If I'm just providing a supply to an isolator I test up to and including the isolator and just make sure that I state on the EIC what I have done and that the isolator is for air conditioning which is being installed by others at a later date.
I know full well that the AC engineers won't do any form of electrical testing or certification.
I think AC engineers should be allowed to install the interconnecting cables but they should be suitably trained and also provide a minor works for the electrical work that they carry out.
Unfortunately if I'm being honest, most of the wiring that I've seen done by AC engineers has been quite poor. No crimped connections and use on non standard cables (SY cables outside with no UV protection).
Not all are bad though, it all depends on the individual.
Also, how do you record the details when the armouring has been used as the CPC for the supply cable and then an internal core/conductor has been used as the CPC for the interconnecting cable?
Doing electrical work for an A/C company who doesn't have a clue is a nightmare!!!
They want the interconnecting cable treated as a separate circuit which is surely incorrect. The whole system is protected by the same MCB so therefore in my opinion it is one circuit???