Discuss Am2 Help Please in the Electrical Forum area at ElectriciansForums.net
Hi, was wondering if anyone could help me please.
just re sat my am2 testing exam but failed because i didn't verify my results correctly to the book and table when they ask on the question sheet through out the exam.
i am hoping someone who has done it recently could point me in the right direction please. or may even remember the questions, i'm just trying to find the correct book, table page, number etc please.
From what i can remember the questions were something a long the lines of;
verify the zs value for the lighting is okay and which book and table you found them in ( i chose the on site guide pg 131)
something about minimun or maximum values of insulation resistance ( i said GN3)
One on disconnection times for certain circuits, (couldn't find the table)
Another was if the breaker would trip within the measured PFC i believe, ( this one threw me) this was a tick box question.
and one on the ring i think to do with zs values again and a calculation, may have been for R1+R2.
sorry it is long and confusing just trying to get any help i can before my re sit on Monday 30th.
Cheers guys, Zack
Did the question mention anything about ambient temperature?
If so did you apply the correction factor in Table B8 page 132 OSG?
Ie B6 amp mcb at 25 degrees Celsius would be:
5.87 (Ohms) x 1.06 (25 degC correction factor) = 6.22 Ohms
So calculated Lighting Zs needs to be a maximum of 6.22 Ohms or less
Table 10.3.3 page 108 OSG
For AM2 exam Minimum 1M Ohm - No Selv or Pelv
Page 59 in the BS7671:2018 Table 41.1
Page 370 in the BS7671:2018
Zs on the ring you measure the rest you calculate
Zs = Ze + (R1+R2)
C32 RCBO Zs 0.55 Ohms Table B6 Page 131 OSG
Hi, thanks for the reply and thank you for the information! One question came back to me, and it was to do when I recorded the highest x5 of the RCD test I think they were asking me to verify or check it to a table, not 100% sure. Would you know what table you is on please?
Reply to Am2 Help Please in the Electrical Forum area at ElectriciansForums.net