Discuss Am2 safe isolation advice in the The Welcome Forum area at ElectriciansForums.net

Reaction score
13
Hi everyone.

I am currently doing my am2. Did they safe isolation today.
Not sure if I messed it up. For some reason I took the protective neutral cover off from the board then performed the 10 step isolation. I asked permission to isolate, labelled with warning signs and put key in pocket. The board had no circuits or even breakers in it. So even if it was live there would of been nothing in the neutral bar anyway. Like I say did everything else ok, just took the plastic protective cover off the neutral bar before 10 point isolation. Am I overthinking? Cheers
 
They could get funny if you could get your probe in the outgoing side of the main switch without removing the cover. If it wasn't mentioned, I'm sure it wasn't picked up on or they thought it was fine though
 
But, there would be nothing on the outgoing. There is a isolator that feeds the board. I turned the isolator off and locked off. The board had no breakers or circuits. So, nothing would ever of been coming through the neutral. Don’t know why I did it. The examiner didn’t say anything, but, then he probably wouldn’t. Just finished first day.
 
Safe isolation is to test that there is nothing on the outgoing side of the main switch, but agree there would be no danger without any breakers/circuits in. How well did you get on with your tutor ;)

Actually, didn't consider reversed polarity before the cu, should of left it on
 
Just nerves more than anything. I was the first person to do it, first thing in the morning. Literally as soon as I did it thought woops. Everything else went good with the install. Just doing my nut in thinking about it. Would be a daft thing to have a retake on. I suppose you can only speculate down to the instructor. He was a sound guy, to be fair.
 
Silver lining is, if I did fail safe isolation. Then I would only have to retake that particular section. Wouldn’t have to do the lot. So, not a massive deal. Just a bit daft! Oh well, life goes on.
 
I wouldn't worry about it too much as you will be tested on safe isolation a couple more times yet.
 
I'm sure the very first safe isolation you perform has to be 100% correct other wise you cannot continue with the assessment. However don't quote me, but I think you may be over thinking it and you'll be fine.
 
I have never done the AM2 myself but have worked with guys and one girl who have, it is sometimes a mystery to me how some of them pass it and others do not, as ultimately i think it comes down to dealing with pressure and the clock in the back of their minds. Its normally silly little things that they would never normally do that causes them to fail. I wish you best of luck for doing it though and hopefully you pass.
 
With 10 steps, I'm presuming it's a three-phase board? I'll go through the steps I'd take to provide some food for thought:
  1. Identify the circuit you will be working on and which corresponding isolator it represents. (In this case however, I'll presume they have asked for the whole board to be isolated).
  2. Ask for permission to isolate, mentioning which circuits will be effected (consider elevators, fire-alarms, lighting, etc) and specify how long until everything is turned on again.
  3. Make sure that you appropriately off-load the board (the main-switch should be last).
  4. Depending on the board, you should either:
    - Lock-off and tag-out, before removing the boards cover (it's preferable but not always possible).
    - Remove the boards cover, then lock-off and tag-out.
  5. Take your AVE (Approved Voltage Indicator to GS38) and perform checks to make sure it's fit for use (look and feel to confirm the condition of body, condition of leads, tips & finger guards compliant, no modifications, fused, etc).
  6. Prove that your AVE is functional by checking it against a known source, listening for the appropriate sounds and visually observing all indicator lights (ideally use a proving-unit for this task, otherwise a known-supply is acceptable).
  7. Complete the 10-step safe-isolation procedure in this order (checks between the safest conductors first and most dangerous conductors last):
    - Earth to Neutral
    - Earth to L1
    - Earth to L2
    - Earth to L3
    - Neutral to L1
    - Neutral to L2
    - Neutral to L3
    - L1 to L2
    - L2 to L3
    - L1 to L3
  8. Re-prove that your AVE is still functional by checking it against a known source, listening for the appropriate sounds and visually observing all indicator lights (ideally use a proving-unit for this task, otherwise a known-supply is acceptable).
  9. Let everyone know that the board has been safely isolated and work can commence. Also advise everyone that you are responsible for holding the key.
I hope this helps and gives you some food-for-thought.
 
Never known it as being 10 step.
Always known it as 12 step.
I'm intrigued Spinlondon, what does the 12 step involve? I'm always responsive to suggestions which improve health & safety in addition to the standard practices.

This was the way I was personally taught in college, the 10 steps only apply to the combination of the conductors (E-N, E-L1, E-L2, E-L3, N-L1, N-L2, N-L3, L1-L2, L2-L3, L1-L3) but doesn't include the other considerations (such as lock-off & tag out, proving AVI before and after, asking for permission, etc) as previously mentioned.
 

Reply to Am2 safe isolation advice in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi I am looking for advice please. Last week I done my am2. And the only thing I failed on was safe isolation of the 3 phase circuit. The...
Replies
11
Views
5K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock