Just done an EICR.
Bonding to water stop cock present.
Bonding to gas. Unknown.
The gas meter is in a cupboard outside. No bonding there. The boiler is on the wall directly behind gas meter and over kitchen cupboards.
I suspect the gas pipe comes in through the wall behind kitchen cupboards and up into boiler. I suspect it is bonded inside behind kitchen cupboards.
Also the boiler pipes have suplimentary bonding across gas water flow return and pressure release. So equal potential of water and gas pipes has been achieved so I am not keen on giving a C2 or FI.
I’m thinking C3
what do you think?