Discuss Another EICR question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Deleted account
Just done an EICR.
Bonding to water stop cock present.
Bonding to gas. Unknown.
The gas meter is in a cupboard outside. No bonding there. The boiler is on the wall directly behind gas meter and over kitchen cupboards.
I suspect the gas pipe comes in through the wall behind kitchen cupboards and up into boiler. I suspect it is bonded inside behind kitchen cupboards.
Also the boiler pipes have suplimentary bonding across gas water flow return and pressure release. So equal potential of water and gas pipes has been achieved so I am not keen on giving a C2 or FI.
I’m thinking C3
what do you think?
I did measure a good resistance back to met, but that may have been due to the supplementary bonding at boiler.
FI does seem a bit harsh, but I don’t know if the gas is bonded as access for inspection is not possible.
in future if boiler is replaced, maybe the suplimentary bonding will be removed as it is no longer necessary in the regs.
I’m still in the FI camp at moment.
I was told off by my NIC inspector last week for putting FI on a condition report due to me not being able to see any bonding wires on the main water pipe.He pointed me to page 475 of the good book section 9 which states that you can only put an FI on the report if the investigation reveals a C1 or a C2. So he was saying it should have been either a LIM or a C3 on the report.Also if you marked it as a FI then the report has to be marked as unsatisfactory.
I usually put C3 with a note that bonding connection inaccessible but confirmed by measurement.
Was there an appropriately sized G+Y single at the MET, that hadn't been identified as the water bond or earthing conductor?
once knew a scotsman. all he wore under his kilt was his wallet.
Reply to Another EICR question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...