Discuss Another RCD tripping in the Electrical Forum area at ElectriciansForums.net
Will a RCD trip if there is a problem on the cable drawing no current ?
I plug in a tumbler drier and power it up, the RCD trips
Remove the drier plug and try the drier in another socket. The drier works without tripping the RCD.
I try my electric drill in the socket that tripped the RCD and at slow speed my drill works increase the revs the RCD trips.
OK I can see the logic here. Its current related More speed, more current, drawn RCD trips.
So will or should a RCD trip if there is a problem with the cable to the socket when there is no appliance plugged into the socket ?
I have just wired up a new extension. The tumbler drier is on a dedicated cct ie it has its own MCB.
There is more !!!!
Same scenario another dedicated cct this time for the freezer. I thought I'd try the drier in that one. I connected this cct up to the drier MCB and flashed the drier up and.............the RCD tripped. Tried the drill same again at slow speed ok increase speed RCD trips.
My immediate thoughts are that the two cables albeit seperate may have been damaged during or after installation.
I guess its time to try and establish that there is nothing wrong with my cable run.
Not sure of your circuitry but
At a guess I would suggest you have a non rcd socket neutral mixed up with the rcd socket neutral
The rcd may very well stay in with no load drawing current
An imbalance of neutrals may give results like you have found
as des says. sounds like a neutral in the wrong bar.
Do the customers that are paying for your profesional services know you are on the net asking a group of random guys how to do your job.
What testing have you done, other than the "bang" test.
I think you are right Des. I have a split box and didn't pay attention when connecting up the neutral(s) well it was late Sunday afternoon.
Yes cables were 'meggered' thru and a ramp test done on the RCD bit low at 25Ma but hey!!
Thanks Des
25mA is quite normal for a 30mA RCD. let us know if it was a N in the wring bar so we can send you to bed with no supper.
Reply to Another RCD tripping in the Electrical Forum area at ElectriciansForums.net
