Ok, so there have been a number of threads on old lighting circuits with no CPC. Also noted that it’s a no no to borrow a route to earth from another circuit.
In this scenario I have two lights atop of brick gate pillars. I have good continuity and sound IR between the two pillars along with a CPC. However there is an armoured feed from the house which comes up under one of the pillars. The end of the amour is not accessible due to concrete and block paving. I have live and neutral conductors but no earth. Would it be acceptable to run a new separate earth conductor back to the origin of the SWA also confirming that the SWA is correctly earthed at the origin?
 