ansell high bay LED x 9 250 watt each b16 or c 16 ? breaker
Discuss ansell LED lights in the Industrial Electrician Talk area at ElectriciansForums.net
Agree, if all the LED fittings are switched on at the same time the inrush current will knock out a B type breaker.C16 every time.
I don't exactly remember why but if are 10 or more LED on at the same time will let the B type tripAgree, if all the LED fittings are switched on at the same time the inrush current will knock out a B type breaker.