Evening,

Visited a site today for an external lighting fault, bollards to be specific.

The circuit contains six bollards and a contactor brought in via a photocell.
Bollards sited around a mill conversion 4 to the front and 2 to the rear.

Protected by a 6A mem rcbo

They rcbo trips whenever the contactor de energises if all the bollards are in cct, if isolate the two to the rear the trip does not occur.
No signs of water ingress.on most bollards, ir testing on the accessible cabling to the rear appears ok, ir tested n-e ok,
The two bollards to the rear show signs of water ingress, had those in bits and checked the connections replaced corroded lamp holders and terminals (bollards are just contain lampholders via fused terminals, no gear in there thankfully)
As soon as any load is added to the rear bollards, it trips.
I can't access all of the cable run to the rear bollards as it's within the mill walls and looks like it goes through atleast one apartment.

Scratching my head on this one a little?

I'm thinking it has an earth leakage problem on this cct, and the wet cold weather has pushed it over the edge.

Any ideas?

Cheers
Nathan
 
Evening,

Visited a site today for an external lighting fault, bollards to be specific.

The circuit contains six bollards and a contactor brought in via a photocell.
Bollards sited around a mill conversion 4 to the front and 2 to the rear.

Protected by a 6A mem rcbo

They rcbo trips whenever the contactor de energises if all the bollards are in cct, if isolate the two to the rear the trip does not occur.
No signs of water ingress.on most bollards, ir testing on the accessible cabling to the rear appears ok, ir tested n-e ok,
The two bollards to the rear show signs of water ingress, had those in bits and checked the connections replaced corroded lamp holders and terminals (bollards are just contain lampholders via fused terminals, no gear in there thankfully)
As soon as any load is added to the rear bollards, it trips.
I can't access all of the cable run to the rear bollards as it's within the mill walls and looks like it goes through atleast one apartment.

Scratching my head on this one a little?

I'm thinking it has an earth leakage problem on this cct, and the wet cold weather has pushed it over the edge.

Any ideas?

Cheers
Nathan
Is the rcbo tripping on a fault or is it the cb part that's causing the trip, ie fault or overload?
 
What about L-E IR? And as above, RCBO needed?
 
Fault not on overload, cct will energise and the trip only occurs when the contactor de energises, all points to an earth neutral fault in my head but can't isolate it
 
I could take the contactor out, but it only trips when the rear bollards are in cct, the remaining 4 bollards are controlled and function via the same contactor.
 
Fault not on overload, cct will energise and the trip only occurs when the contactor de energises, all points to an earth neutral fault in my head but can't isolate it
Poor Neutral connection somewhere, done any earth leakage clamp testing??
 
Don't rule out leakage in Photo cell ,
(that you may be reluctant to IR too heavily)
--Sounds marginal somewhere,
+ Spike from contactor !
..Hence like try without contactor comment...
 
All CFL lamps
I did consider the photocell but as an after thought after I'd left the site,
all good points thanks. I'll be revisiting next week couple of additional items to check on site and then I'll be back onto this one.
 

Reply to Any ideas, on this one.. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
839
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hi Folks, have just finished replacing an old fuseboard with a new rcbo jobby. To say there have been a few surprises would be putting it mildly...
Replies
12
Views
1K
Got called to "a flat in Manchester has no hot water" at 16:30 today and to be frank I was a little miffed to have to attend. So arrives at site...
Replies
67
Views
7K
I’d like your opinions on a scenario I’ve come across. A certificate was produced which contained errors and while there were still faults on the...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock