Hi
I am having my garden landscaped and using the opportunity to put services in a trench in preparation for a garden studio/office build in the summer.May put a shower and water heater in as well.Approx 55 meters from house fuse board to office location.
What size of armoured cable should I use ?
 
Hi - with 55m + to cover, the determining issue will likely be voltage drop. You’ve mentioned you’d like a shower and a water heater. So a decision is whether you will use a tank and 3kW immersion heater for your hot water or an instant (on demand) heater of say 10kW. If you then add another load of say 2kW for lights, computer and a small heater we’ve got say 21A or 50A depending. No prizes for guessing the big load will need a bigger cable :) .
 
Hi - with 55m + to cover, the determining issue will likely be voltage drop. You’ve mentioned you’d like a shower and a water heater. So a decision is whether you will use a tank and 3kW immersion heater for your hot water or an instant (on demand) heater of say 10kW. If you then add another load of say 2kW for lights, computer and a small heater we’ve got say 21A or 50A depending. No prizes for guessing the big load will need a bigger cable :) .
Hi
Water heater fairly unlikely, building will be divided between secure shed and a room, use yet to be determined. Two oil filled rads. A few sockets and LED down lights

16 or 25mm ?
 
As you will have to get the installation tested and signed off by an electrician, your best bet would be to get one involved from the start. Design is one of the sections to be signed on the certificate.
It will save you a lot of grief later on.
 
  • Agree
Reactions: DPG
Easy........25mm SWA will cover all your CCC and VD worries in lieu of calculations and having a design current! Design is for softies anyway.......With cables, it's a case of go big or go home!! Lol
 

Reply to Armoured cable size in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Trying to find an armoured cable behind plasterboard and studding. It was used to supply power from the house but has been disconnected Can...
Replies
2
Views
421
Hi All, I hope you are doing ok. I have a question regarding the 24V system. I am going to build a pergola and I could install 4 panels on it...
Replies
10
Views
562
Hi all. I've recently bought a bungalow. It currently has a armoured cable between the house and garage which spans less than 1 meter. The height...
Replies
4
Views
1K
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock