Hi All,

I have a job to install 6mm supply to a small outbuilding. Ideally i would run SWA all the way from Meter box(im taking it from Henley block) to the outbuilding, but not in this case. Cable will have to go through the kitchen area. So im thinking to have 6mm t&e in trunking, it's only about 4 meters. But my concern is that this cable has 2.50mm earth conductor as opposed to 6mm on swa. Another option is to run 3 singles in the trunking, all 6mm. Is that good practice?
Any help would be great
 
What do your design calculations tell you?

Also your splitting the tails, what protection are you going to use?
 
Either way you can’t take a 6mm csa cable straight off a standard 100a cut-out via Henley blocks.
the entire submain will require suitable overload protection and rcd protection.
you will need to install some sort of single way consumer unit to provide both.
 
What do your design calculations tell you?

Also your splitting the tails, what protection are you going to use?
Current design is fairly small not more then 20A based on maximum demand.
Yes, i have to split tails, its TNCS system there is a spare terminal for main earth conductor at the service head so i can use when connecting swa at the meter box. Protection: 40a double pole rcbo inside the meter box in the small 2 module consumer unit
[automerge]1596830288[/automerge]
Either way you can’t take a 6mm csa cable straight off a standard 100a cut-out via Henley blocks.
the entire submain will require suitable overload protection and rcd protection.
you will need to install some sort of single way consumer unit to provide both.
Yes, im fitting small CU with 40a rcbo inside meter box, just didn't mention that
 
It needs to go through inside for about 4m. I found solution. I cut section of swa, removed outer sheath and steel armour and fit remaining 3 cores with inner sheath in trunking. So I've achieved continuous 6mm earth connection.

As long as it is fully enclosed in the trunking it is OK. That inner sheath is not a sheath, it is bedding, so it must be installed with the same protection as you would for single insulated cables.

How did you gland and earth the SWA cable for this arrangement?
 
As long as it is fully enclosed in the trunking it is OK. That inner sheath is not a sheath, it is bedding, so it must be installed with the same protection as you would for single insulated cables.

How did you gland and earth the SWA cable for this arrangement?

Its fully inclosed in 25 x 25 trunking. Ive used outdoor swa glands and adaptable box, as well as fly lead to connect steel armour and earth
 

Reply to Armoured cable & T&E in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
503
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
530
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
601

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock