Hi, my Consumer Unit is in a cupboard in my hall. I would like to install 1 double socket only in this cupboard.

I was wondering if I could run the cable to feed this socket from an already occupied 16amp mcb or 32amp mcb from within my CU?
 

Dustydazzler

Regular EF Member
Messages
1,036
Location
Surrey
Hi, my Consumer Unit is in a cupboard in my hall. I would like to install 1 double socket only in this cupboard.

I was wondering if I could run the cable to feed this socket from an already occupied 16amp mcb or 32amp mcb from within my CU?
Technically you can nick a feed from an already in use mcb.
But if you have a spare slot then just whack in a new 16a mcb for the new plug socket
 
OP
P

pckid57

DIY
Messages
8
Location
Scotland
Technically you can nick a feed from an already in use mcb.
But if you have a spare slot then just whack in a new 16a mcb for the new plug socket
Thanks for the reply. I'm not sure if I have an empty slot yet. If not is it safe to "Nick a feed from an existing mcb"?
 

Grant1987

EF Member
Messages
15
Location
Aberaman
Hi, my Consumer Unit is in a cupboard in my hall. I would like to install 1 double socket only in this cupboard.

I was wondering if I could run the cable to feed this socket from an already occupied 16amp mcb or 32amp mcb from within my CU?
Hi, yes you can do that at the consumer unit aslong as you havnt already spured off from your consumer unit the regs say an unfused spur May be connected to the origin of the circuit at the distribution board
 
  • Like
Reactions: DPG

Grant1987

EF Member
Messages
15
Location
Aberaman
Hi, yes you can do that at the consumer unit aslong as you havnt already spured off from your consumer unit the regs say an unfused spur May be connected to the origin of the circuit at the distribution board
Or preferably just put it on its own circuit as dusty dazzler said
 
OP
P

pckid57

DIY
Messages
8
Location
Scotland
Hi, yes you can do that at the consumer unit aslong as you havnt already spured off from your consumer unit the regs say an unfused spur May be connected to the origin of the circuit at the distribution board
So it's okay to run a 2.5mm twin & earth from the existing mcb straight to the new intended socket, which is about five feet away from the CU?
 

westward10

In echoed steps I walk across an empty dream.
Staff member
Moderator
Messages
11,549
Location
Northamptonshire
Put in a new protective device it would require notification to building control under Part P of the Building Regulations. Connected from the existing ring final circuit it does not, that's the way of it. Do you have rcd protection.
 

ipf

Forum Mentor
Messages
4,859
Location
Walmington-on-Sea/Lancashire
Put in a new protective device it would require notification to building control under Part P of the Building Regulations. Connected from the existing ring final circuit it does not, that's the way of it. Do you have rcd protection.
…….and are you sure all is in order with the existing ring circuit, if there is one. A bit of testing wouldn't go amiss.
 
OP
P

pckid57

DIY
Messages
8
Location
Scotland
Put in a new protective device it would require notification to building control under Part P of the Building Regulations. Connected from the existing ring final circuit it does not, that's the way of it. Do you have rcd protection.
Yes there is RCD protection. The new socket will only be used to charge s Dyson Hoover.
 

westward10

In echoed steps I walk across an empty dream.
Staff member
Moderator
Messages
11,549
Location
Northamptonshire
Put in a new protective device to a spare way requires notification to building control, this is a legal requirement. Some responses to this thread have not considered this.
 

Grant1987

EF Member
Messages
15
Location
Aberaman
See #7, this
Put in a new protective device to a spare way requires notification to building control, this is a legal requirement. Some responses to this thread have not considered this.
Hi, no I didn’t consider if it was going to be notified i assumed he was going to comply with regs and I’m new to forum and I can quickly see that people without relevant qualifications may just want to do DIY without it being properly tested and certified so my bad will make sure future responses are compliant
 

GeorgeCooke

Regular EF Member
Messages
487
Location
UK
If the new socket is near the CU. Remove one of the legs of the ring from the CU MCB and put it in your new socket. Run a short length of 2.5 T & E from you new socket back to the CU MCB. Thus the new socket becomes part of the ring.
 

Pete999

Forum Mentor
Messages
21,840
Location
Northampton
You can only have 1 unfused spur from any point of circuit including consumer unit that’s the regs.
You can only have 1 unfused spur from any point of circuit including consumer unit that’s the regs.
I think what that reg means is that you can take an unfused spur from anywhere on the RFC, including at the CU, you are guilty of misinterpreting the Regulations Grant.
 
OP
P

pckid57

DIY
Messages
8
Location
Scotland
Hey George Cooke, that sounds a good idea, it would obviously be good to add the new socket to the Ring, I'm still trying to visualise that setup in my head, the job is actually in my sister-in-laws house. That being the case; would I only need to remove the live from the mcb and put it in the new socket, leaving the neutral in the neutral bar? Then run a 2.5 t&e from the new socket, doubling the live with the live I've removed and put in the socket, and putting the new neutral and earth in the appropriate bars in the CU?
 
OP
P

pckid57

DIY
Messages
8
Location
Scotland
Westward explain why, i was only trying to confirm what someone else suggested. You appear to be very negative, no pun intended.
 
OP
P

pckid57

DIY
Messages
8
Location
Scotland
Ok, I'm not an electrician. I'm looking for advice, I have a basic knowledge of Electrics, but believe with the correct advice I could do jobs like the one I'm asking about.
 

westward10

In echoed steps I walk across an empty dream.
Staff member
Moderator
Messages
11,549
Location
Northamptonshire
Westward explain why, i was only trying to confirm what someone else suggested. You appear to be very negative, no pun intended.
Whilst the forum doesn't mind giving advice to DIYers we do not extend that to step by step advice. From your posts this task is beyond your scope of knowledge. Leave it to a professional.
 

harryspadge

EF Member
Messages
9
Location
Aldershot
Ok, I'm not an electrician. I'm looking for advice, I have a basic knowledge of Electrics, but believe with the correct advice I could do jobs like the one I'm asking about.
I would suggest you take a look at a diagram or a ring circuit so you can fully understand how it works before attempting what you intend.
It's not easy giving advise to someone when it's not clear of there level of knowledge and undertsanding.
Sorry, not trying to be negative !
 

Grant1987

EF Member
Messages
15
Location
Aberaman
Which regulation is that?
Appendix 15
Ring and radial final circuit arrangements
Regulation 433.1
Page 505 have a look at the diagram it illustrates all that you can do with regards to spuring off very good page to understand the dos and donts as I wasn’t too sure untill I seen that page.
 

tony clark

gaslec instalations
Messages
46
Location
essex
to many google diyers out there thinking they know it all just by asking questions on forums. a friend of mine had a customer thinks he knows it all does all his own wireing dosent even know how to cable size volt drop loves a jb and choc blocks apprantly
i was told his garage caught fire. insurance refused to pay out because electrics was all wrong, little knowledge is dangerous,
 

SJD

Forum Mentor
Messages
1,040
Location
Braccan heal
Appendix 15
Ring and radial final circuit arrangements
Regulation 433.1
Page 505 have a look at the diagram it illustrates all that you can do with regards to spuring off very good page to understand the dos and donts as I wasn’t too sure untill I seen that page.
Appendix 15 is an informative annex, it is not normative. It shows some options that can be used for ring and radial final circuits. You can have multiple unfused spurs on the ring (you can find a few discussions about this on this site).
 

Grant1987

EF Member
Messages
15
Location
Aberaman
Appendix 15 is an informative annex, it is not normative. It shows some options that can be used for ring and radial final circuits. You can have multiple unfused spurs on the ring (you can find a few discussions about this on this site).
Sorry I’ve not made it clear what I was trying to interpret yes you can have multiple unfused spurs on any circuit but only one at each point didn’t make it clear find it easier to explain in person rather than txt
 