Discuss AVI (Approved Voltage Indicator) - Common Misconceptions in the Electrical Tools and Products area at ElectriciansForums.net

I2C

-
Reaction score
56
Hi Guys!

I've worked with a few qualified-electricians recently and I'm shocked with the large-scale misconceptions regarding the proper safe-isolation procedure, particularly concerning the function of an AVI (Approved Voltage Indicator).

During the last few weeks I've met several domestic qualified-electricians who have told me not to test between line-earth & neutral-earth because this will trip the RCD/RCBO; they have all advised me to only test between line-neutral. When I confronted them with actual facts and figures, they all refused to acknowledge my comments, arguing otherwise without any form of proof, which I found bizarre?

I'd like to confirm that their advice is incorrect, and I can prove it factually. I use a Kewtech KT1790 Approved Voltage Indicator which seems fairly common amongst electricians, and I'll base my comments on this:

  • The Kewtech KT1790 data-sheet states "This instrument can make measurements between L-PE without tripping RCDs".
  • The Kewtech KT1790 data-sheet states that the devices internal-resistance is 200,000 Ohms. Based on this value, we can calculate the current-flow using basic Ohm's Law:
    - 230V - 1.15 mA (Standard RMS voltage used for design calculation)
    - 245V - 1.22 mA (Highest likely RMS voltage measured)
    - 500V - 2.50 mA (Exceeding AC Peak Voltage)
  • A common RCD used in domestic properties for additional-protection has an operating-current of 30mA (much greater than the current produced while testing).
  • Rarely in specialised circumstances a 10mA RCD is used for certain applications (much greater than the current produced while testing).
To conclude, the AVI (Approved Voltage Indicator) is perfectly suitable and safe for use when performing the proper safe-isolation procedure (including testing between line-earth and neutral-earth) as explicitly explained within the products data-sheet, and also proven through simple calculation of it's specifications.

I'm interested to find out if anyone else has encountered this problem? If so, to share this information.
 
See page 18 of pdf

Niceic pocket guide 5

It clearly says to test between:

Earth and Line
Neautral and Line
Earth and Neautral
 

Attachments

  • Best-Practice-Guide-2.pdf
    1.1 MB · Views: 15
They've had experience of older basic testers (pre LED) which did trip RCD / RCBO and not bothered to try with the newer non trip ones.
 
I've worked with a few qualified-electricians recently and I'm shocked
You say you are shocked, so much for safe isolation. If someone you work with wishes to chance getting an electric shock just make sure you know appropriate resuscitation techniques. Apart from warning someone what can you do. As for Popular Misconceptions, it certainly has not been my experience that this is endemic in the trade most people I have met take all due precautions. I also add to persons who sometimes work/train with me that they should test between local metal work and earth to ensure there are no stray voltages such as suspended ceilings when working on klik fittings above. I have found 120v on suspended ceilings before. So think about that as well.
 
The Fluke T-150 has an RCD trip function built in, so you can test at a circuit and trip the RCD by pressing two buttons (one on the dumb probe and one on the main unit).

But regardless, they are wrong. Safe isolation requires a full test of L-N, L-E and N-E.
 
shoot them down with this then.

example is a lost N, so test L-N, no reading. then get a belt off the L. maybe their thinking is because L-E and N-E tests are covered in week 6 of their 5 week course.
 
First they are very very wrong
Second,my advice for anyone interested, learning or even qualified in electrics, it is to never under any circumstances accept assurance off anybody but yourself that something is safe or even advice on how to make something safe

Its your health and well being at stake and its too important to trust to anybody irrelevant of whether they appear to know what they are doing
 
And even when you know it is off , work as if it isn't.

Sir, I think this would be worth elaborating for EF readers giving examples of what you do. The electricians doing our current extension wore dextrous rubber gloves for example - the plumbers wore similar gloves more I think for the grip and prevention of cuts.

It might be these:

Ansell ActivArmr ActivArmr Electricians Gloves Grey Large - https://www.NoLinkingToThis/p/ansell-activarmr-activarmr-electricians-gloves-grey-large/99723

The organisation I worked for taught the 'one hand rule' for example to avoid across the chest/heart shock currents.
 
Last edited:
And even when you know it is off , work as if it isn't.

The obvious one is to always use insulated snips for cutting cable, even if you know it's dead. One day it won't be.

Same for insulated screwdrivers. If you get into the habit, then it won't go so badly for you when, eventually, you tighten a terminal that should be dead, but isn't.
 
i always check tightness of terminations when live. if it sparks, it's not right. therefore the vde drivers are a must, otherwise i might get a tingle that wakes me up.
 

Reply to AVI (Approved Voltage Indicator) - Common Misconceptions in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
1K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
398
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
916
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock