doing an eicr
I noticed the cable feeding the service head on 3rd floor from ground floor is a 1x25mm awa cable
From the service head 3rd floor it’s your normal tails to dB in flat
So the awa cable is being used as below
The inner core used as line
The outer sheath (unsure on mm size of this anyone?) is being used as neutral and earth
Does anyone know about this set up as I haven’t seen it before?

AB8A8698-EC2C-44AF-B171-BA0126E28254.jpeg
 
AWA stands for Aluminium Wire Armour and the line core can be copper or aluminium.
Yes, usually used with 3 phases to prevent eddy currents and made off into an Aluminium gland.
The AWA usually has a lower CCC than the core, as it is only being used to provide earth fault protection.

Not sure a reduced CCC would be acceptable when the AWA is being used as a PEN conductor.
 
I don't think it is AWA. If it has an aluminium core and is concentric the outer conductor is likely to be copper.
 
Are you sure it’s AWA, not copper concentric?
Aluminium conductors are usually larger than Copper and require special lugs for terminating.

It doesn't always need special lugs, barrier grease can be used to terminate aluminium into brass terminals. This is how DNO's terminate aluminium concentric cables into standard cutouts.
 
I don't think it is AWA. If it has an aluminium core and is concentric the outer conductor is likely to be copper.

Yes I can see the outer core is copper but I can’t See if it’s aluminium inner core, it’s terminated.
What would the csa of the outer copper sheath be , if the inner core is aluminium 25mm ,(this is being used for cpc and neutral
 

Reply to Awa cable? Any information would be helpful thanks in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
734
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
714
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock