• Please checkout this (ad-free) update post I've done on a spare blog. Feel free to bookmark it and check everynow and again for update if ads are pissing you off. Always feel free to ad-block them for now though if you want. I'll let you know when you can disable the ad blocker again, only if you want to see the ads. They should look nice and neat in the end.

Discuss Bad shock off Hot Tub. in the Electrical Forum area at ElectriciansForums.net

Reaction score
0
Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Got called out to look at a hot-tub. (reasonably new I think) which client was getting a shock off. Have tested everything up to the panel in the Hot Tub. RCD is fine although hasn't tripped when under load. It is when the main motor kicks in that water become's live. Most likely a fault with the Hot Tub itself but with the callout charge I want to make sure. Anyone have any experience with this. What else could it be?
 

telectrix

-
Mentor
Esteemed
Arms
Reaction score
67,260
rigourous testing will find. does sound like a hot tub fault. any road. customers that can afford the leccy to run these things deserve shocking.
 

UNG

-
Mentor
Esteemed
Arms
Reaction score
5,223
What supply type do you have and how have you tested that the water becomes live
How is this hot tub earthed and what is the Zs of the supply?
How are the pump(s) and heater earthed?
Have you checked for earth connections / continuity on the electrical equipment on the hot tub
 

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,335
What supply type do you have and how have you tested that the water becomes live
How is this hot tub earthed and what is the Zs of the supply?
How are the pump(s) and heater earthed?
Have you checked for earth connections / continuity on the electrical equipment on the hot tub
6 questions within 4 sentences, not bad.
The answers will be interesting.
 

Gavin John Hyde

-
Esteemed
Arms
Patron
Reaction score
5,158
Given the amoutn of hot tubs that have been bought since this pandemic began and number of enquiries I get regards running a circuit - i am usually too busy thankfully . It is about the right time we start getting threads on the forum about them causing issues. either poorly installed or dodgy parts in them.
Sadly I wouldn't be surprised if somebody does get a fatal shock one day as I was told for one I did quote for that I was too expensive and some fly by night outfit did it for £150 - the materials would have been £80 mind..
 

UNG

-
Mentor
Esteemed
Arms
Reaction score
5,223
6 questions within 4 sentences, not bad.
The answers will be interesting.
Should I have asked more??

One of the big issues is earthing and the "just knock a rod in and TT it" brigade. All well and good not exporting the earth if understand what you are doing but just putting a rod in can create other problems if a fault occurs when you have water and wet people in the area around the rod and tub
 
OP
P
Reaction score
0
What supply type do you have and how have you tested that the water becomes live
How is this hot tub earthed and what is the Zs of the supply?
How are the pump(s) and heater earthed?
Have you checked for earth connections / continuity on the electrical equipment on the hot tub
The supply is PME which initially made me think that it could be broken PEN but tested and it seem's fine.
Hot tub wired in armoured all the way. Plastic board. Armoured glanded into box above CU. Earth on sheath wasn't earthed but have put that right today.(was picking up about 50-60v off the sheath.) Induction most likely. Armoured run is about 15m from the house into a rotary isolator. Isolator look's ok. Zs seemed within normal range if slightly higher than expected. They have spurred off the hot tub supply to feed some light's in the decking. (fused spur next to rotary iso) which made me think could that be anything to do with it (bit dodge). DIdn't even start looking at the hot tub itself. Just wanted to confirm it wasn't the wiring before calling an engineer out. Was debating putting an earth rod in but will see what the engineer says first. In the hot tub itself the armoured is just in a cord grip no gland needed wouldn't know where to start with pump's ,heater etc. Never encoutered such thing ever before it was like the wall and the ground was all live pretty worrying/playing on my mind tbh.
 

UNG

-
Mentor
Esteemed
Arms
Reaction score
5,223
The supply is PME which initially made me think that it could be broken PEN but tested and it seem's fine.
Hot tub wired in armoured all the way. Plastic board. Armoured glanded into box above CU. Earth on sheath wasn't earthed but have put that right today.(was picking up about 50-60v off the sheath.) Induction most likely. Armoured run is about 15m from the house into a rotary isolator. Isolator look's ok. Zs seemed within normal range if slightly higher than expected. They have spurred off the hot tub supply to feed some light's in the decking. (fused spur next to rotary iso) which made me think could that be anything to do with it (bit dodge). DIdn't even start looking at the hot tub itself. Just wanted to confirm it wasn't the wiring before calling an engineer out. Was debating putting an earth rod in but will see what the engineer says first. In the hot tub itself the armoured is just in a cord grip no gland needed wouldn't know where to start with pump's ,heater etc.
Have you actually confirmed the hot tub is properly earthed as it reads like you have only checked Zs at the isolator

Have you tried an earth leakage clamp on the mains to check if there is any earth leakage or at what level it is at

If you treat the hot tub as an appliance and test it as such what results do you get especially the testing of the earth bond from the supply point to the heater and pump(s)

Never encoutered such thing ever before it was like the wall and the ground was all live pretty worrying/playing on my mind tbh.
Have you confirmed this as a fact
 

Reply to Bad shock off Hot Tub. in the Electrical Forum area at ElectriciansForums.net

Similar Threads

Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
729
  • Question
Hi, My hot tub keeps tripping after 12 years of use. I'm thinking it's the GFCI gone bad. Unfortunately it's a CH 2 pole 50 amp (GFTCB250) and...
Replies
1
Views
589
Hi, looking for some advice, 6mm swa allready installed to a hot tub Client now wants additions and my calcs say the original swa is allready too...
Replies
26
Views
2K
Hi I posted recently about a hot tub supply I was needing advice with. One reply I got was directing me to a video by dave savery. Having...
Replies
9
Views
2K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...