S

simbin

I've recently been approached to do the electrical installation on a barn conversion, no problem straight forward! The problem is getting a supply in. The owners want to have the mains coming from their cottage about 23 metres away. They don't want the driveway digging up for a new supply as its only just been block paved. Is there anyway of separating the supply in the cottage or do they need a site visit from electric supplier to determine whats required???:)
 
And the power comes from???? Split meter tails in henly block?! Surely 100A fuse can't supply two consumer units??? (cottage & barn)
 
Its not too big-kitchen,lounge,one bedroom,bathroom. All electric, no gas. 3 panel heaters,hob, oven. SO.....25mm tails from isolator split in a henly block to feed consumer unit in cottage & metal clad switch fuse with swa on out going side is fine??
 
The cottage is PME. The following circuits to be installed; Shower (40A),Cooker(32A),Upstairs ring-8 points(32A),Downstairs ring-14 points(32A),Upstairs Lights-6 points(6A),Downstairs lights-6 points(6A),Smoke alarm-2 points(6A)
 
The cottage is PME. The following circuits to be installed; Shower (40A),Cooker(32A),Upstairs ring-8 points(32A),Downstairs ring-14 points(32A),Upstairs Lights-6 points(6A),Downstairs lights-6 points(6A),Smoke alarm-2 points(6A)

And the barn?
 
The cottage contains; Shower(40A),Cooker(32A),Upstairs ring-13 points(32A),Downstairs ring-14 points(32A), Kitchen ring-8 points(32A),Lighting circuit-13 points(6A)

Just been looking at the forum, there's one on there about exporting earths......a mixed bag indeed! Who's right,who's wrong?!?!?
 
Last edited by a moderator:
The mains water into the barn is through one big ugly piece of plastic, so no earth required.

Thanks to Bugsy & Pennywise for much help & guidance.:) I will go for splitting the meter tails & terminate into a 63A switch fuse but without putting a spike in. Thanks once again.:D
 
Last edited by a moderator:
You will still need to earth the water at the first piece of copper after the poly pipe enters the barn or get the plumber to put in a small length if he's doing the whole lot in plastic. cheers
 

Reply to Barn conversion in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
274
  • Sticky
A recent thread on the suitability of a cable supplied preinstalled on a manufactured floodlight/pump had me wondering a few things. Over the...
Replies
4
Views
856
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock