Evening all

Posted this in blogs by mistake!!

Bit baffled with current situation, maybe someone here has experienced before?
Just wired up a bathroom light with the extractor fan as normal practice. All works fine until light is switched off and during the 15 minute over run the light blinks on and off every few seconds. when the fan is switched off at the isolater the blinking stops, so it definately has something to do with the fan wired via the switch live. Any thoughts before i start fault finding?

Thanks
 
Evening all

Posted this in blogs by mistake!!

Bit baffled with current situation, maybe someone here has experienced before?
Just wired up a bathroom light with the extractor fan as normal practice. All works fine until light is switched off and during the 15 minute over run the light blinks on and off every few seconds. when the fan is switched off at the isolater the blinking stops, so it definately has something to do with the fan wired via the switch live. Any thoughts before i start fault finding?

Thanks

what make and model fan is it?
 
Definitely voltage getting back to the light via the fan then. I would guess at either the perm live touching the switched live at the fan, or a faulty circuit board in the fan.
 
an, but didn't moses part the brown sea. the bible said red, but europe says brown. shows what heathens the EU are.
 
Not if it is touching but not connected. Seen plenty of cables over the years making an intermittent contact. I'm sure that you have too with all your experience Moses :)

You don't mean touching, but adjacent to each other, but electrically separate, hence allowing electromagnetic pickup.

The lamp will only flicker if its a CFL.

May be the OP should try an incandescent lamp and see if it still flickers.
 
You don't mean touching, but adjacent to each other, but electrically separate, hence allowing electromagnetic pickup.

The lamp will only flicker if its a CFL.

May be the OP should try an incandescent lamp and see if it still flickers.

No, I mean TOUCHING. Sometimes, when cables are connected to small terminal blocks such as one finds in fan units, it is not uncommon to find that someone has stripped too much insulation off, or even that there is a strand from a stranded cable touching an adjacent cable.

Why are you always so obtuse Moses? Do you like just winding people up are do you have a superiority complex?
 
Some interesting theories there lads. There is definately no touching of wires anywhere. Fan is a Airflow Q100HT. What i did try though was to pull the switched live from terminal 1 (delayed start/15 min over run/humidity) and place in terminal 2 (constant run) and bingo, no light flicker, BUT dissappointing as it was purchased for the delayed start and humidity control! Prob looking more likely that there is a prob with the board. The bulb is a CFL so i will dig out a incandescent lamp in the morning and see if that has any impact.

Thanks so far
 
No, I mean TOUCHING. Sometimes, when cables are connected to small terminal blocks such as one finds in fan units, it is not uncommon to find that someone has stripped too much insulation off, or even that there is a strand from a stranded cable touching an adjacent cable.

Why are you always so obtuse Moses? Do you like just winding people up are do you have a superiority complex?


Not being obtuse. sorry if it comes across as that way.
But if the switched wire was touching the permanent then the lamp would stay ON? or not?
 
Not being obtuse. sorry if it comes across as that way.
But if the switched wire was touching the permanent then the lamp would stay ON? or not?

The Pd would be the same, therefore no.

Edit: Just realised that's wrong, the light could potentially stay on if the union was downstream of the switch.
 
Last edited:
The Pd would be the same, therefore no.


May be I am not understanding what you are trying to explain.

As the switched wire connects the 230V from the switch to the lamp, to supply the L to the Lamp to light it, and then this switched L is fed to the fan. So if this switched wire connects/shorts to the permanent L in the fan, then surely that permanent L connects through the switched L to the lamp supplying it with 230V. The Lamp already has a permanent N, and now has a L.

I am sure if the Permanent L and Switched L were connected/shorted any where then the lamp would stay on.

What PD are you talking about?
 
May be I am not understanding what you are trying to explain.

As the switched wire connects the 230V from the switch to the lamp, to supply the L to the Lamp to light it, and then this switched L is fed to the fan. So if this switched wire connects/shorts to the permanent L in the fan, then surely that permanent L connects through the switched L to the lamp supplying it with 230V. The Lamp already has a permanent N, and now has a L.

I am sure if the Permanent L and Switched L were connected/shorted any where then the lamp would stay on.

You are correct, hence my previous edit.
 
Not being obtuse. sorry if it comes across as that way.
But if the switched wire was touching the permanent then the lamp would stay ON? or not?

After a 4 year apprenticeship and over 20 years in the field, there have been many times when I have come across cables "touching" without being connected, causing intermittent supplies to loads. This can often be caused by vibration, and would result in a "flicker" in this instance.
If this is a difficult concept for you to understand then I can only apologise for confusing you with my suggestion.
 
Replaced the CFL with a low watt halogen and hey presto! all works fine according to plans. Absolutely no flicker. Big thank you to Moses for the idea, saved a lot of hassle. This is one of those scenarios that nobody can teach you so many thanks to all members for input.
 
I had this problem once on a job for a council in a school, after a lot of head scratching it turned out that my mate had marked up the cables wrongly. Stripped everything out, traced which cable was which reterminated and it worked fine.
 

Reply to Bathroom light/extractor fan problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
694
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
1K
Just had the following extractor fan fitted for my bathroom, recommended by my electrician. Based on the manual it states the fan should be...
Replies
3
Views
400
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
648

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock