pburley

Hi guys replaced a bathroom pull cord five months ago, it was damp inside but broken so I replaced. Went back today and inside is damp and slightly corroded. pull cord is near (abouit 8 inches) from shower cubicle. Do they make IP rates pull switches? Ceiling is solid concrete with steel conduit so not easy to move switch. Any ideas guys. Many thanks:)
 
I am not aware of IP rated pull switches, but then i have never looked for one. I do know that there are IP rated occupancy detectors which you could use to replace the pull switch, but you will need a neutral to it. They are PIR and can be set for about 20 minutes, i use them in HMO's communal bathrooms and toilets so the tenants dont leave the lights on forever. Its down to whether or not your customer will be happy.

Cheers........Howard

PS, Plan B, seal switch terminals with some silicone sealant.
 
Last edited by a moderator:
Sound to me as if the pull cord is in zone two so should be moved should be 0.6 meters from zone two check the onsite guide to be sure
 
If it is above 2.25M above floor level then it is outside zones.
 

Reply to Bathroom pull switch in the Australia area at ElectriciansForums.net

Similar Threads

This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
929
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi, I wish to get a rough estimation of how much a job should cost considering the UK: Supply and install 44 Led downlights in ceilings Rewire 9...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock