Discuss Bear with me on this one in the UK Electrical Forum area at ElectriciansForums.net
cliffed
Supporter
So if you supply a external lamp post(metal),the metal is an exposed conductive part,& connected to the cpc,no main bonding required.
If you add a socket or a light to an external remote metal shed,will this need main bonding,or the cpc on the power point or light will suffice.
It’s an actual aleady extraneous part,with its structure embedded to earth.
If a shed is an extraneous conductive part with electrical accessories and wiring installed then no the cpc on a light or socket will not do at all regarding satisfactory protective bonding, how the hell would it?
An external lamppost will be classed as an exposed conductive part, if it was to introduce an earth potential then to provide protective bonding to it is pointless and unnecessary as it’s located directly outside, so you could never maintain or create an equipotential bonding zone being directly stood on the ground and all.
When I was a member of the ILE a debate took place as to whether the column of a lamp post could serve as an electrode for the purpose of staking PME supplies. The suggestion was no because most columns are treated at low level to prevent corrosion and as such may not be effective.
Understand,so does the shed need Main bonding,it’s more like an open porch than a shed ie: no doors,just frame work.
It’s external,& like you said being stood on the ground outside.
Would that be referenced as a true earth,unlike extraneous conductive parts,which may introduce a potential.
When I was younger, I used to install lamp posts.
In order to be able to connect to the REC PME earth connection, we had to install an earth electrode (usually at the penultimate column).
Depending upon which REC we were dealing with, determined how low our RA had to be.
South Eastern, just wanted an electrode, the LEB wanted an RA of 10 Ohms.
Yea,can understand all these comments,we didn’t fit the socket,it’s on an industrial estate,the main supply is a 1,200 amp Pme system,so definitely an earth potential there.
The actual main bonding conductor is 50mm.
Why would you need an earth connection with a gas lamp ??
This would have been concrete columns?
You do realise, it was during the Napoleonic wars that they first installed electric lamp posts in London?
wrong. napoleon was defeated in 1815. London first got electric streetlights late in the century.
I'd say it's standard spec throughout the country -certainly for L.A. 'adopted' street lighting that the column has a 10mm main bonding conductor connected to the MET, the steel columns all have a terminal near the door opening for this. I know that in Cornwall at least 95% of the supplies are PME and when you consider your average 8 or 10 metre column on busy routes has a 'planting depth' of between 1.2 and 1.5 metres it's not going to do the RECs ELI any harm eh ?:)
Reply to Bear with me on this one in the UK Electrical Forum area at ElectriciansForums.net
Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Seen many answers on this but still not sure on a definite answer. Power installed inside metal container, the units inside a warehouse, the...