Discuss Best way to deal with moisture in cable in the UK Electrical Forum area at ElectriciansForums.net

The continuity readings should be similar. If they are both correct (which they quite probably aren't) then the high one appears too high, because for 6mm² T&E cable R1 +R2 should be around 0.01Ω/m. 0.88Ω implies the cable is over 80 metres long which surely isn't correct. 0.15Ω looks entirely plausible, therefore the excess of 0.63Ω could indicate a high-resistance joint in the neutral that will heat dangerously under load (at 20A that's 252W, the heat of ten soldering irons)

The insulation resistance L-E at the fault seems to fall in the middle of the two ranges on the tester, off the bottom of the scale for IR (reading 0.01MΩ or lower (you can't tell how low when the display is showing the lowest possible number other than zero) but off the top of the scale for the continuity test. This is a limitation of most MFTs but we don't really need to know the actual resistance as it's definitely no good as it stands.

So what we can infer from the readings if they are all correct is that the insulation of the line is seriously low, possibly low enough to overheat dangerously, while the continuity of the neutral is seriously high, possibly high enough to overheat dangerously. The readings don't enable the location of the damage to be narrowed down.
Thanks, You are right -
New readings for Continuity:
LE 0.11 ohms
NE 0.12 ohms

(Dodgy crocodile clips I think: will use WAGO connector in future).

IR results are the same.
 

Reply to Best way to deal with moisture in cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Hi all, My first post here, thought I'd see if it was possible to get some advice or tips... Basically, I had a large amount of block paving and...
Replies
80
Views
12K
I'm reading a thread at the moment about a 9.8kW shower that has been installed on a 6mm cable. My natural instinct was to think that's wrong, it...
Replies
22
Views
6K
I do seem to pick only the weirdest properties to inspect... Victorian terraced house today - with up front RCD to a Wylex fuse board and main...
Replies
24
Views
3K
Is there a room in professional PAT testing for a business model other than 'per unit'? I ask because I've been giving this some thought. I've...
Replies
40
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock