RFC step 1 tests :- l-l .31Ohms, n-n .31 Ohms, cpc-cpc 0 Ohms, repeated this numerous times and got same results. Remove crocodile clips from probes and touch cables directly and get sensible results. Repeated this exercise a few times as it didn't make sense to me but kept getting the same readings. Electrician co-worker did exactly the same (repeatedly) and got the same results (with my Ethos mft - he didn't have his mft with him).
Obviously I know the solution but any thoughts on the reason as I am now tending to give credence to the poltergeist theorists?
 
I'd be giving credence to the CEF theory, Ethos are a City Electrical brand aren't they?

There again, what are the sensible results and how are you touching direct?
 
This is on initial verification so, basically, just checking my own work where I would expect to have end to end continuity.
I was expecting the cpc end to end results to be higher than the live conductor results.
Touching direct was achieved by placing the bared conductors on a piece of wood and pressing the probes hard, my body not being in contact with the bare probes or bare conductors.
Just cannot understand why the meter will measure correctly without the crocodile clips but with them it shows a dead short on the cpc but not on the lives. cpc-cpc 0 Ohms, l-l .31, immediately back to cpc where it reads 0 again, immediately back to a live and .31.
 
I'm making an assumption here that you do actually have a continuous, non-shorted cpc on the ring, and it measures (if the other results are to be believed) somewhere around .45 ohms?

And also that your meter is doing an R1-R1 to R2-R2 each at a time on some kind of setting?

Three options - either knacked leads/clips, knacked software on the meter or a knacked operator.

And, if you're in the position of testing your own work, I'd really like to sleep better knowing that you don't need help to figure out which of those three it is.

Clue: do the test again on a known value of conductor / proving card, and just use the R1 settings for all conductors. You may need an old fashioned tool called a pen to write down the results instead of having the machine save them.
 
You may need an old fashioned tool called a pen to write down the results instead of having the machine save them.



or a slate and stylus.

 
I test as I go. The tails are clearly visible for about 5m. There is no short circuit as proved by not using the clips.
I am able to test. I have the 2391.
The question is not about my competency although we can all make mistakes.
The problem occurs when using the clips. As already stated I know the solution - replace the clips. However I do not understand why I am getting the correct reading on the live conductors but not on the cpc when using the clips but I get what I expect when not using the clips.
Yes the meter is set to the correct scale, yes I null the leads when changing between with and without the clips.
I replaced the batteries in the meter when I first got these readings but it made no difference
 
No, but thanks for a constructive reply.
I know that everything is all fine. It tests out perfectly when not using the crocodile clips. Cpc-cpc is .51 Ohms from memory without the clips (and leads correctly nulled). With the clips (again correctly nulled) it will not read this figure but displays 0 yet transfer the leads to either the l's or the n's and I get a reading of .31 Ohms.
I just don't understand how this can be. It is not just me either as my friend was giving me a hand on this job (also 2391) got exactly the same results and was equally as mystified.
 
I would invest in another Low Ohms meter as a back up if nothing else.

As you have pointed out the test results are what you would expect but now doubt has been put in your mind re the connection of the clips.

I had a issue with my leads and croc clips on a Megger I use but it was the spring connection on the probe that was worn which was not seating inside the clip correctly to make a sound connection!
 
It seems to be a mystery but I'm sure it's not. Not the sort of question to put forward here, I feel.
 
No, but thanks for a constructive reply.
I know that everything is all fine. It tests out perfectly when not using the crocodile clips. Cpc-cpc is .51 Ohms from memory without the clips (and leads correctly nulled). With the clips (again correctly nulled) it will not read this figure but displays 0 yet transfer the leads to either the l's or the n's and I get a reading of .31 Ohms.
I just don't understand how this can be. It is not just me either as my friend was giving me a hand on this job (also 2391) got exactly the same results and was equally as mystified.

Hum.... did you do another check else where on the ring?? I certainly wouldn't be happy with what you are seeing.
 
crap gear

My fluke did exactly the same a couple of times. I broke out my personal IR tester (megger) and it was fine. Dumped the fluke, M1552 sorted, never looked back. Fluke said you gotta do this n that, I said jog on.
 
I test as I go. The tails are clearly visible for about 5m. There is no short circuit as proved by not using the clips.
I am able to test. I have the 2391.
The question is not about my competency although we can all make mistakes.
The problem occurs when using the clips. As already stated I know the solution - replace the clips. However I do not understand why I am getting the correct reading on the live conductors but not on the cpc when using the clips but I get what I expect when not using the clips.
Yes the meter is set to the correct scale, yes I null the leads when changing between with and without the clips.
I replaced the batteries in the meter when I first got these readings but it made no difference

You're getting a result of half an ohm over a 5m run of cpc (presumeably 2.5T&E) in a ring??!! Come on man, THINK!
 
I have never used Ethos gear, just wondering what symbol it uses to show an open circuit on continuity tests, it isn't an O by any chance? Or did the tester actually say 0.00 ohms for the reading?
 
You're getting a result of half an ohm over a 5m run of cpc (presumeably 2.5T&E) in a ring??!! Come on man, THINK!
Try READING. If I can see 5m of perfectly undamaged sheathed cable I can see that there is no dead short for at least 10m, therfore, even if there was a dead short just out of sight, I would expect a reading of 19.51 x 10 mOhms. Have you ever heard of a 5m ring main??!! Come on man, THINK!
 
Try READING. If I can see 5m of perfectly undamaged sheathed cable I can see that there is no dead short for at least 10m, therfore, even if there was a dead short just out of sight, I would expect a reading of 19.51 x 10 mOhms. Have you ever heard of a 5m ring main??!! Come on man, THINK!

Yep.....as I thought. What's the resistance of 10m's of 1.5mm2 copper conductor? (Try looking it up)
 

Reply to Bizarre readings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
841
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K
No photo's as customer is already in dispute with kitchen fitter and was very strict about it! I went to look at what would be involved to add a...
Replies
3
Views
1K
Hello, looking for some advice on 2 things please. Ive tested a ring main in a house with RCD protection, the results ive had are L-L .43 N-N...
Replies
24
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock