Discuss Board change query. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
R
roukel01
Morning everyone
Just a quick one.
What do you guys do when doing a board change and you come accross a 9.5Kw shower on a 40amp MCB wired in 6.0mm? Its not clipped direct so current capacity tables show that its less than the 40amp MCB.
when you say not clipped direct, is the cable in insulation or buried in a masonry wall?
pull insulation away from on top of cable.leave some airspace around it. i'd also clamp the shower and see what it pulls.
edit: and i'd check the cable in the loft for any signs of overheating.
Do the calcs, drop down to 32 (or whatever) if necessary and advice the customer that the cable may need upgrading or could face nuisance tripping on the new breaker (you'll probably have to explain to them why you had to change it as well)
Que 6mm 9.5kw shower thread :)
Reply to Board change query. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
4K
Hi. I'm being tasked with installing an electric shower into a property that was built back in the 1980's. The main consumer unit has only 4 ways...
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...