Hi all

Been asked to quote for a board change. Had a quick look round the place and discovered lighting circuit has no earth. Where do I stand on this?

Current board is 3036s and will be replacing with rcbos as wiring is quite old. Will also be bonding the gas and water from 4mm to 10mm.
 
lighting circuit is ok as long as it doesn't have any class 1 fittings or switches on it reconnect it to new consumer unit and make note on certificate

That's what I think as well, but I notice that the Best Practice Guide is a little more flexible than that if the customer refuses to replace Class I fittings or rewire the circuit / install a protective conductor, maybe a little too flexible?
 
The esc cu guide actually allows you to fit a new consumer unit even with metal unearthed fittings

as long as they are not outside or within reach of any extraneous conductive parts

but you must perform an IR test between the live terminal and the meatallic casing of the fitting i think if memory serves correct?
 
The esc cu guide actually allows you to fit a new consumer unit even with metal unearthed fittings as long as they are not outside or within reach of any extraneous conductive parts
The ESC is not in a position to allow or forbid anyone to do anything. It is a guide.

but you must perform an IR test between the live terminal and the metallic casing of the fitting i think if memory serves correct?
Are you sure? What would that prove, other than it was not live when you tested it?
 
The esc cu guide actually allows you to fit a new consumer unit even with metal unearthed fittings

as long as they are not outside or within reach of any extraneous conductive parts

but you must perform an IR test between the live terminal and the meatallic casing of the fitting i think if memory serves correct?

Would recommend if you post somthing like this, that backing it up with a link to the approprate documentation would help.
 

Reply to Board change with no cpc on lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
791
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock