Thanks Dartlec,

It is for rental property, 3 actually. My problem is that I retired 10 years ago and now live in France so can't get back easily to take care of things.
I worked commercial so never had experience in houses or EICR's. The 1 bedroom flats were all bought like this. I did have the CU's changed in 2 of them 5 years ago. I know the make/model of the fan so I'll write to Xpelair, see what they say.
I hear you about C2's meaning potential danger, I'm struggling to see how a plug top suppying a boiler or lack of isolator (except the breaker) on a fan is going to cause any danger :)

What do you think about his comment that 7671 having new editions changes things. By his reckoning rewirables should be getting C2's now. No? Or do they? It was always my belief (wrongly?), that if it was once in the regs you couldn't give it a C2.

Cheers,

Keith.

There are some things that were once fine according to the regs, that are now C2 - though a lot of them are related to very old methods of fusing, or wiring that is crumbling due to age - or the lack of an cpc for lighting circuits prior to 1966...

The situation with EICRs is complicated, partly because BS7671 doesn't properly address it and leaves it to 'guidance'. The testing is to current regulations, but things that are not as per current regulations are not automatically a code (There used to be a Code 4 that was dropped).

If a property was installed correctly as per regs say even 30 years ago, then there is not going to be much that should reach a C2, based on current guidance. Lack of RCD protection on sockets that might supply outdoor equipment and bathroom circuits is the main one that crops up.

Rewireable fuses are not themselves an automatic failure (Though personally they really should be gone in rental properties these days) - but boards that age often haven't had RCD protection added, which is where a C2 can reasonably be applied.

The other issue is that many flats/houses, including some done recently, do not comply with the Regs that were in place at the time... The classic example is single insulated twin and earth cores visible at downlight terminations.
 
@KeithC it might be worth mentioning what rough area the property is in, someone nearby might be willing to have a quick look around to form their own view/2nd opinion and subsequently do another EICR.
 
There are some things that were once fine according to the regs, that are now C2 - though a lot of them are related to very old methods of fusing, or wiring that is crumbling due to age - or the lack of an cpc for lighting circuits prior to 1966...

The situation with EICRs is complicated, partly because BS7671 doesn't properly address it and leaves it to 'guidance'. The testing is to current regulations, but things that are not as per current regulations are not automatically a code (There used to be a Code 4 that was dropped).

If a property was installed correctly as per regs say even 30 years ago, then there is not going to be much that should reach a C2, based on current guidance. Lack of RCD protection on sockets that might supply outdoor equipment and bathroom circuits is the main one that crops up.

Rewireable fuses are not themselves an automatic failure (Though personally they really should be gone in rental properties these days) - but boards that age often haven't had RCD protection added, which is where a C2 can reasonably be applied.

The other issue is that many flats/houses, including some done recently, do not comply with the Regs that were in place at the time... The classic example is single insulated twin and earth cores visible at downlight terminations.
Thanks for your help.

Cheers.
 
So......

Regarding the plug and socket for isolation. There is no issue with a socket and plug being used for isolation (except in bathrooms) however this needs to be double pole isolation. The switch on the socket is only single pole and it is very likely that when isolating the device the switch would be used rather than the plug being removed.

An unswitched socket outlet then. Coz any gas safe enginner wouldn't know to unplug the boiler. FFS.
 

Reply to Boiler Isolator in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock