The present small job is in a unit, one of 40, in a single story Victorian mill.
The construction is cast pillars and beams in a roughly 6 meter grid
I cannot find any evidence of the steel being bonded, the site is huge and it seems unreasonable to spend days sorting this for a few sockets.
Where tested all the steel returns a result of 0.0MOhms (IR 500V) between the test spot and CPC of the incoming distribution circuit, a 5 core 25mm SWA, all parallel paths omitted.
So it is either bonded or Extraneous.
Is there an issue with just running a 25mm bond to the nearest steel, check continuity at various places, and being done.
Or is there a concern, that if the steel is not bonded, that fault currents from elsewhere on site will effectively flow through 'my' DB?
Hope this makes sense.