Why would you be relying on next doors bonding? It either needs bonding or the resistance is of that that it doesn't need bonding, effectively seperate from earth.
 
Because its a separate property on a separate supply.
Also you never know what the might
Happen in the future as to pipe work.
Bonding is required in each property to bring all parallel paths to the
Same potential.
Obviously sometimes this isn't required if there are no parallel paths
 
can understand what your saying,i would bond it tho,like you say who knows what can happen in the future?plumber turns up to change pipe work next door fits plastic or doesnt refit the clamp?leaves all the pipework in your property
unbonded,assuming it is copper piping
 
so in a block of eight flats, each one has its own meter and fuseboard, there is one main incoming water off the street which branches off to each flat, just bonding the incoming water?? to which MET would you bond it to then?
 
so in a block of eight flats, each one has its own meter and fuseboard, there is one main incoming water off the street which branches off to each flat, just bonding the incoming water?? to which MET would you bond it to then?
I have just looked at a job that fits this scenario. There is a 50mm copper riser with meters sprouting of it on each floor in the stairwell. At the moment there are two 6mm bonding cables clamped to a couple of the branches one of which goes to the power head of the flat I am concerned with. The copper pipework within the flat is being renewed and I propose fitting a 10mm bond at the kitchen stopcock back to the MET WITHIN the flat. Am I correct in this course of action.
 
Separate supplies with separate MET's then it will need bonding, exactly the same as in block of flats. Doesn't matter how close the 2 conection points are, you treat each individual dwelling as a separate entity!!
 
Separate supplies with separate MET's then it will need bonding, exactly the same as in block of flats. Doesn't matter how close the 2 conection points are, you treat each individual dwelling as a separate entity!!

But as Tel said earlier on, what if someone stuck a piece of plastic in between? It would depend how atractive the next door neighbour is.

I'd do exactly what you say.
 
Last edited by a moderator:
I have just looked at a job that fits this scenario. There is a 50mm copper riser with meters sprouting of it on each floor in the stairwell. At the moment there are two 6mm bonding cables clamped to a couple of the branches one of which goes to the power head of the flat I am concerned with. The copper pipework within the flat is being renewed and I propose fitting a 10mm bond at the kitchen stopcock back to the MET WITHIN the flat. Am I correct in this course of action.

Yes, each separate flat should be treated as separate place.
As e54 said.

Obviously you need to check that each separate flat needs bonding with your tester.
If there's no parallel path to earth no need to bring it to the Same potential.
 
But as Tel said earlier on, what if someone stuck a piece of plastic in between? It would depend how atractive the next door neighbour is.

I'd do exactly what you say.

This case is a little different from blocks of flats, in that the Granny flat is attached to the main building and uses an extension of the house water service, where flats would be taken individually from a main riser feed. But seeing as the two separate unit's are owned by the same homeowner the chances of a plastic pipe isolating the units is to be honest remote. You could always make the homeowner aware, that if any plastic pipe is inserted into the water service between the two units he will need an electrician to test the Granny flat. So to ascertain if the service in that unit still remains extraneous or not, (over 23Kohms) if it's not, the bonding conductor and clamp needs to be removed!!
 
I have spoken to great white oracle ( who takes my money every year so I can be in their gang ) & he informed me that I should bond the water pipe where it enters the flat to the cu in the flat. So that is what I will do, many thanks for all the answers & comments.
 
Hi
Can somebody tell me what earthing arrangments are at the origin of both supplies?, for example if the house supply earth was PME and the flat earth was TT then as things stand you could be introducing a different earth potential back into the main house as the water pipes are connected at the moment. A solution may be for earthing purposes is to install a piece of plastic pipe from the main house where it enters into the flat this would seperate bonding pipework and earth potentials, although there still could be implications within the common water.
 
Hi
Can somebody tell me what earthing arrangments are at the origin of both supplies?, for example if the house supply earth was PME and the flat earth was TT then as things stand you could be introducing a different earth potential back into the main house as the water pipes are connected at the moment. A solution may be for earthing purposes is to install a piece of plastic pipe from the main house where it enters into the flat this would seperate bonding pipework and earth potentials, although there still could be implications within the common water.
Or just install bonding as per the requirements of BS7671.
There could be difference in potential even if both installations are PME, just the same as with neighbouring properties in a terrace.
 
Last edited by a moderator:
Id be bonding both flats seperately. I think if you test you'll find the water could be an extrenupus part. They are two seperate supplies with two seperate earths.

Sent from my GT-I9100 using Tapatalk
 

Reply to bonding conundrum in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
519
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
850
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock