We all know that armed cables should be bonded but I have inherited a job of a so called electrical contractor. My problem is he as ran 2 core 16mm SWA to 3 flats with a separate 16mm earth but the SWA has not been glanded off, and it’s a finished job.
I can not pull out and start over so does any one know of any other way to earth the armouring without glanding off. Please no Tenby earth straps
 
Hi.

In short no. To effectively earth the armourings glanding off is the only way. Are the armoureds surface run or hidden in walls?? Could you not install a metal adaptable box above/below the CU and gland into that?? contiunuing the cores through and earthing the armoudes that way??
 
Not entirely sure, but I think he has covered bases with the use of a seperate CPC. Table 54.7 quotes that if csa of phase is 16mm or greater, then the CPC must be the same CSA. By running a separate he is complying.

It is not an exposed part as it is sheathed.

I stand to be corrected (not shot down).

Dave
 
this is not my recomendation they do need glanding, but if you are in a muddle you could strip some outer off to expose the armour, you could solder a fly lead on each end and terminate it that way (rough though)
 
Luckily as it's not the circuits cpc only one end needs bonding, so as markspark666 suggests you could strip the outer sheath then pull the strands to one side, trim them to the same length and find a crimp lug that's a good fit.

It won't look very smart but perhaps you could find something to overwrap the whole thing.
Richard.
 
albi is there any reason why you can,t isolate i know it could inconvienence the client but it seems like it,s not your fault,and lets face it both you and the client want a good job done
yours benji
 
If it was only that easy I would not off been asking the question but no the SWA is all behind plastered wall (finished) and about 20mm showing. As I am only issuing a periodic for the job to building control it will have to go down as a departure.
My fist thoughts where to go down the lines of what is used in the jointing kits i.e. sprung steel and earth brads any thoughts on that as i only need to protect the SWA from any impac(nails/screws)
 
when i first used the coiled spring clamps i thought they were **** but changed my opinion as the do get a good hold and visualy they would look better than a tenby ,but you would have to use an earth braid and could you term the braid into the earth bar in the cu.
is the cable plastered into the wall and if so is it protected in any way
yours benji
 
Last edited by a moderator:
yes its plasterd in with no protection apart fron the 80amp fuse at the fused isolater at the meter end this is my consern as i only need to earth the SWA not the final cu as this is coverd by the sepoarate 16mm earth wire
 
Has anyone ever used these, I've seen them used in lamp posts but I've never been able to find anywhere that sells them.
 

Attachments

  • 12072006140.jpg
    87.9 KB · Views: 44
  • 12072006142.jpg
    76 KB · Views: 39
  • 12072006143.jpg
    94.2 KB · Views: 35
See BS7671 522.6.6 (i) Incorporate an EARTHED Metallic covering etc etc cables complying with BS5467 SWA
So armouring must be earthed even if not being used as a CPC
Reg 134.1.1 Good workmanship by competent persons ..... proper materials.........Equipment shall be installed in accordance with the instructions provided by the manufacturer....
The cable should be properly terminated in accordance with manufacturer instructions = GLANDED both ends and SWA earthed as should any other exposed conductive part.
I suggest you dig it out and do it properly if thats part of the contract otherwise report it on the PIR as an observation and recommend cable is correctly terminated
 
Go with the earthing coiled springs and braid. I wasn’t impressed with them the first time I used them in joints but when I tested them before sealing the joint I changed my mind. The one I used had half moon sectors that went around the inner serving and pushed down under the armourings then the clamp went around the whole lot, they were absolutely sound.
 
Yep used them myself many times with both braid and multi stranded flexible cable, with a heat shrink breakout overall covering the earth termination and the complete end of the cable.

All SWA cable terminations on high end projects will incorporate heat shrink cable breakouts, they seal the cable completely against any moisture ingress.
 

Reply to bonding for swa in the Australia area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
I'm working on a system that has been installed incorrectly. It's a 3ph Hager board with 8 swa cables glanded into the bottom entry panel. The...
Replies
28
Views
3K
Is anyone aware of any galv trunking that is smaller than 50x50. I'm drawing a blank online. I've taken over a job that's used 16mm twin and earth...
Replies
12
Views
778

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock