Hi Guys,
I was going to use the following as a part of my assessment with niceic next month but I'm at a quandary.

The job was to swap a spurred socket outlet with a FCU and spurr off that to two double sockets, one next to the FCU in the hall and the other in the living room on the other side of the wall to which the first was installed.
I've upgraded the earthing conductor to a 16mm² and the main bonding conductors to 10mm² except for the water services.

I tested from a disconnected main bonding conductor at the MET to the water stop cock valve body and the highest measurement attained was 0.04 ohms. This figure seems too low (6mm² and at least 10m long possibly more) and leads me to believe a parallel earth path exists. Also the conductor has green (not g/y) insulation and is 6mm² (should be 10mm²).

Here's my issue: The kitchen has been fitted impressively. I mean all the pipes etc. were jointed after the units were installed. Perfectly formed, circular holes in the back of the sink cupboard. I've never seen such impressive workmanship.
I know, now, that I shouldn't have installed the extra sockets until the earthing arrangements were upgraded but that's history.
The owner of the property is not happy for me to start destroying his lovely kitchen and I'm reluctant to do so. Can I record a limitation?

I'll be very grateful if any of you can help.
 
What would you expect the resistance to be for 10m of 6mm² single core cable (e.g. from the OSG tables)?
 
Why bother if the 6mm is ok? I think the op point is it installing it that is going to be pig of a job

I agree but as the OP says it is for a assessment, just for the sake of a few meters of cable it would be worth doing especially as he has already renewed the gas bond. Also the assesses can sometime be picky, but the maybe he could use a few regs numbers to back his argument up on why he didn't upgrade it.
 
They can be as picky as the want but if it complies as per the regs then if it not reasonably practical then I wouldn't be doing it. As above though bE prepared to have some evidence for things you have noted on the cert .

However what earthing system is it?
 
Aype.. I had that on my first one. gave him the cert for the job and used the printable ones off IET site.. Anyway first think he said was ahh these dont comply... Really, No there not in the correct format.. Anyway page whatever of the regs and guess what the identical form.. That shut him up
 
Thanks for all your suggestions. I have several balls in the air at the moment and unable to sit in front of my computer.
It's a tn-s system.
I haven't checked the conductor resistance yet but I will a bit later when I've dropped some of the balls.
 
Aype.. I had that on my first one. gave him the cert for the job and used the printable ones off IET site.. Anyway first think he said was ahh these dont comply... Really, No there not in the correct format.. Anyway page whatever of the regs and guess what the identical form.. That shut him up

Interresting! I have not used the niceic forms, I've used the downloadable forms from the iet which I believe are replicas of those in the bgb.

Back in a while...
 
What would you expect the resistance to be for 10m of 6mm² single core cable (e.g. from the OSG tables)?

0.03 ohms - took my eye off the ball and manage to double it before!

... that solved that bit of the equation; moving on...

The gas and power are supplied in a garage. The water, according to the owner, is at the other end of the house.
There's a boiler in the garage and all the pipes disappear upwards. The existing water bonding conductor goes into plastic trunking and it too disappears upwards (not in the same place).

If I could replace the existing conductor without damaging anything I would. But if there's a less destructive solution, all the better for all interested parties.
 
. The water, according to the owner, is at the other end of the house.
There's a boiler in the garage and all the pipes disappear upwards. The existing water bonding conductor goes into plastic trunking and it too disappears upwards (not in the same place).

If I could replace the existing conductor without damaging anything I would. But if there's a less destructive solution, all the better for all interested parties.

why not bond across all of your boiler pipes, including water, make a note on the cert
 
If I could replace the existing conductor without damaging anything I would. But if there's a less destructive solution, all the better for all interested parties.

Why haven't you carried out an adiabatic equation? Chances are the csa of the water bond is fine as is.
 
Correct, so on a TN-S system to size a bonding conductor the main earthing conductor must be sized correctly. The OP said he just whacked in some 16mm but I would bet he gave this very little thought. The amount of times I've actually put in a 16mm MEC in a domestic situation because of requirement I could probably count on one hand.

Chances are, the original 10mm MEC was absolutely fine. If so, he could leave the 6mm main bond in place.
 
Correct, so on a TN-S system to size a bonding conductor the main earthing conductor must be sized correctly. The OP said he just whacked in some 16mm but I would bet he gave this very little thought. The amount of times I've actually put in a 16mm MEC in a domestic situation because of requirement I could probably count on one hand.

Chances are, the original 10mm MEC was absolutely fine. If so, he could leave the 6mm main bond in place.

You're absolutely correct (and you win the bet), I didn't think too much about installing 16mm² for the MEC because I thought I had to! Have I misunderstood something somewhere?
I'm going to read chapter 54 in the bgb again. I've lost count how many times I've read it, and unfortuneatly the misunderstood is sticking.
 
In short the MEC is a protective conductor, therefore it can be sized using an adiabatic equation. The bonding conductors can then be sized as not less than half the REQUIRED size of the MEC. TN-S system that is. Ergo sum, if the required size of the MEC is less than 10mm, then your main bonding conductors can be 6mm.
 

Reply to Bonding water services in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
665
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...
Replies
2
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
772
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock