Scratching my head a bit on a job today. Been to clients house to investigate fault with installation.
For the past few months client has reported that both RCD's on his dual RCD board have tripped at the same time on odd occasions thus losing all power to house.
House was rewired by another contractor few years back. TN-C-S earth.
It happens at all different times of the day and night and the RCD's reset with no problems afterwards too. Only happens maybe once a month or even less than that.
Went today to have a look and carried out Insulation Resistance tests. First a global test between N-E bars then for each individual circuit N-E & L-E.
-Circuits protected by left RCD were all fine. Lowest IR reading obtained was about 50Mohm which quickly rised to >99.9 during test
-Circuits protected by right RCD had low IR readings on two of the socket circuits. cct2 0.63Mohms and cct3 2.63Mohms
Both ccts were fine once all items were unplugged. IR readings went up to >99.9. Likely culprit(s) seems to be the numerous surge protection extension leads and IT equipment in home office in cct2.
Both RCD's tested and trip times were fine and ramp tests showed they tripped at 25mA
Carried out IR test between both Neutral bars and interestingly I did get a reading of about 60Mohms quickly rising to >99.9Mohms. Narrowed this down between cct's 2&3 on right side with cct7 (sockets) on left side.
All end to end readings on socket circuits were fine and as mentioned above all IR readings with wiring seem fine once everything was unplugged.
Bit of a loss to what would cause both RCD's to trip at same time. Opinion is that all the IT equipment is enough to occasionally trip the one RCD but can't think why both would trip.
Only time I've seen both RCD's trip is when borrowed neutral is present or wrong connections in consumer unit after a change, so the random nature of them both tripping is confusing me a bit.
I'll stress that I haven't actually witnessed this symptom happening but him and his wife are adamant that both trip at same time.
Is there anything external to the installation that can cause both RCD's to trip at same time or any else I could look out for. I've asked them again to take notes if it happens again and recommend to remove surge extension leads where not really necessary.
Thanks for reading and any help would be much appreciated.
For the past few months client has reported that both RCD's on his dual RCD board have tripped at the same time on odd occasions thus losing all power to house.
House was rewired by another contractor few years back. TN-C-S earth.
It happens at all different times of the day and night and the RCD's reset with no problems afterwards too. Only happens maybe once a month or even less than that.
Went today to have a look and carried out Insulation Resistance tests. First a global test between N-E bars then for each individual circuit N-E & L-E.
-Circuits protected by left RCD were all fine. Lowest IR reading obtained was about 50Mohm which quickly rised to >99.9 during test
-Circuits protected by right RCD had low IR readings on two of the socket circuits. cct2 0.63Mohms and cct3 2.63Mohms
Both ccts were fine once all items were unplugged. IR readings went up to >99.9. Likely culprit(s) seems to be the numerous surge protection extension leads and IT equipment in home office in cct2.
Both RCD's tested and trip times were fine and ramp tests showed they tripped at 25mA
Carried out IR test between both Neutral bars and interestingly I did get a reading of about 60Mohms quickly rising to >99.9Mohms. Narrowed this down between cct's 2&3 on right side with cct7 (sockets) on left side.
All end to end readings on socket circuits were fine and as mentioned above all IR readings with wiring seem fine once everything was unplugged.
Bit of a loss to what would cause both RCD's to trip at same time. Opinion is that all the IT equipment is enough to occasionally trip the one RCD but can't think why both would trip.
Only time I've seen both RCD's trip is when borrowed neutral is present or wrong connections in consumer unit after a change, so the random nature of them both tripping is confusing me a bit.
I'll stress that I haven't actually witnessed this symptom happening but him and his wife are adamant that both trip at same time.
Is there anything external to the installation that can cause both RCD's to trip at same time or any else I could look out for. I've asked them again to take notes if it happens again and recommend to remove surge extension leads where not really necessary.
Thanks for reading and any help would be much appreciated.