I have done a few of these jobs for the same client. Install a 315a fused TPN isolator in their new heating centres. All the others I have done UKPN have bought in a PME supply so I have just mounted the fused isolator with tails into the CT chamber ready for me to do the follow up at a later date so the meter man can get his stuff on and get it live. This one I have gone to and no earth has been supplied no problem I say to the client I will put your earth rod in and an rcd unit as the first point, which I was under the impression was required. The client then calls the meter man who has connected the previous five for us where the connections come from the PME on the head and the terminals from the CT chamber but he is saying that there is no need for the rcd unit on the TT system. Am I missing something here?

I have but the rcd unit in as I am sure it needs it just picking people's brains incase there is some reg I am not aware of or is the British gas guy clueless?
 
Cheers bud. Didn't have my regs book on site with me but I'm going to find the reg stating this just so I can justify the extra cost and materials compared to the others I have done for him.
 
Why do people listen to these meter merchants, most of them know even less than a Electrical Trainee!!

Because in the eyes of the clients they are the gods that turn their power on to their nice new district heating exchange. Which if is not on in time has a £1.9m penalty clause involved.
 
Technically he is right and our learned friends above are wrong.There is no reg stating an RCD is required on a TT. 411.5.2 states that an RCD is the preferred means of earth fault protection,not a required means. If a TT provded a low enough Ze value then an OCPD could be used.Of course in the real world......Oh no,hang on,everyone keeps telling me they get sub 1 ohm Ra values so why the RCD?
 
Technically he is right and our learned friends above are wrong.There is no reg stating an RCD is required on a TT. 411.5.2 states that an RCD is the preferred means of earth fault protection,not a required means. If a TT provded a low enough Ze value then an OCPD could be used.Of course in the real world......Oh no,hang on,everyone keeps telling me they get sub 1 ohm Ra values so why the RCD?


The Clever arse rises again......lol!!

Unfortunately that sub 1 ohm value can ''only'' be achieved when people put a little effort in and ''TRY''!! It will rarely to Never happen with people like you, (who has never achieved anything even close) who have clearly made it clear on many occasions here, that you have no intention of ever trying because the BGB say's 200 Ohm, and that's good enough for ANY of you lazy buggers out there!!

It's the drose like the above that makes the UK literally the worst country i've ever had the pleasure to work in for TT systems. It's funny how other countries can routinely provide stable single and low double figure Ra values and in UK triple figures are what's aimed for, especially if it happens to be under that somehow magical 200 Ohms mentioned in the BGB!! ....
 
The Clever arse rises again......lol!!

Unfortunately that sub 1 ohm value can ''only'' be achieved when people put a little effort in and ''TRY''!! It will rarely to Never happen with people like you, (who has never achieved anything even close) who have clearly made it clear on many occasions here, that you have no intention of ever trying because the BGB say's 200 Ohm, and that's good enough for ANY of you lazy buggers out there!!

It's the drose like the above that makes the UK literally the worst country i've ever had the pleasure to work in for TT systems. It's funny how other countries can routinely provide stable single and low double figure Ra values and in UK triple figures are what's aimed for, especially if it happens to be under that somehow magical 200 Ohms mentioned in the BGB!! ....

Just found it interesting that in post #6 the implication is that by stating that the meter man is spouting nonsense,your view is that an RCD is required. Why not say to the OP that a proper TT electrode will provide a low enough Ra to negate that requirement?
 
Just found it interesting that in post #6 the implication is that by stating that the meter man is spouting nonsense,your view is that an RCD is required. Why not say to the OP that a proper TT electrode will provide a low enough Ra to negate that requirement?


No, you just thought you'd try being a clever dick again!! lol!!

I stated that most of these metermen know less than a electrical trainee. But i can just guess as to what the earth rod installation is like and the sort of Ra value that has been obtained!!

Now if this district heating project has such a high monetary value, there shouldn't be any financial restrictions to actually providing a sub 1 ohm TT system, but will it ever get such a TT installation?? Very doubtful in the UK, after all there is always an RCD to bung in!!
 
No, you just thought you'd try being a clever dick again!! lol!!

I stated that most of these metermen know less than a electrical trainee. But i can just guess as to what the earth rod installation is like and the sort of Ra value that has been obtained!!

Now if this district heating project has such a high monetary value, there shouldn't be any financial restrictions to actually providing a sub 1 ohm TT system, but will it ever get such a TT installation?? Very doubtful in the UK, after all there is always an RCD to bung in!!

Cop out mate.
 
WP, you're just lazy!

Everybody knows that 10 ohms is better than 200 ohms. Of course, there will be absolutely no difference whatsoever in how the system operates, but 10 is lower than 200, so it must be better?!

;-)
 
No, you just thought you'd try being a clever dick again!! lol!!

I stated that most of these metermen know less than a electrical trainee. But i can just guess as to what the earth rod installation is like and the sort of Ra value that has been obtained!!

Now if this district heating project has such a high monetary value, there shouldn't be any financial restrictions to actually providing a sub 1 ohm TT system, but will it ever get such a TT installation?? Very doubtful in the UK, after all there is always an RCD to bung in!!

how can you obtain a steady sub 1 ohm reading which you can guarantee not to fluctuate due to weather drying up ? will the circuit meet its 0.2s or 1s disconnection times depending on circuit design?
just a question...
 
how can you obtain a steady sub 1 ohm reading which you can guarantee not to fluctuate due to weather drying up ? will the circuit meet its 0.2s or 1s disconnection times depending on circuit design?
just a question...

In certain areas, subject to ground conditions, it can be done, and very easily. I have done it, as will have any electrician worth his salt. It won't ever have been on a domestic though that's for sure. Last time I did it was at the intake building for a large agricultural installation.

Ten or so underground sub mains fed from the intake position. It was either a decent earthing system or £2k for an up front s-type for the whole complex, which in itself would have been idiotic.
 

Reply to British gas TT earthing and rcds in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Replies
1
Views
373
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
855
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
790
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Ukpn have put a supply in for us to feed an outside cabinet, which will eventually supply foul water, sewage pump's. They have supplied an earth...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock