9.3KWWas waiting for why. Basically there is 5 plug in appliances (totalling 9.3 KW including tea urns, coffee machines, fridge, 2x kettles which a vicar needs to be on simultaneously, once in a while. One circuit would be easier to run than two.
With 9.3KW ,Ib=40.4a so In >=40aDoes anyone know if its acceptable to have the ocpd of a radial circuit serving only single sockets higher than 32A ?
2 x 6mm would be the most a socket could take so probably 40A OCPD (singles in trunking).
9.3kw
9.3KW
With 9.3KW ,Ib=40.4a so In >=40a
It>=43a assuming ambient temperature is 35°c.
If you use reference method A (enclosed in conduit in an insulated wall) you are going to end up with a10mm cable which i think is expensive and difficult to terminate in a radial.
So i suggest you split the load into 2 radial circuits with Ib = 20a each wiring in 2.5mm.You can use 4mm as well with the same ref.method which is also expensive compared with the 2.5mm.