My curiosity started when filling in an EIC and wondering the difference between BS 1361 & BS 88-3.
Without paying the eye-watering prices for copies of the standards, I just don't know. There was a useful summary table in this with both standard's Zs limits given:
Then I wanted to know about what different capacities they has regarding to types and use.
But that's when it got confusing looking at the different types in the OSG Appendix B and trying to find out their uses and differences.
The BS 1361 & BS 88-3 also don't need the same PFC capacity as industrial work might demand. I think they are in the 16.5kA for the "type 1" fuses, those from 5-45A seen in some fuse boxes till the 80s that a home owner might change, and 33kA for the "type 2" range from 60-100A for cut-outs that one would hope the home owner does not change!
One other difference I did notice is the older standard would have 15, 30, 60A, and the new one 16, 32, 63A like MCBs.
Where as the industrial BS88-2 fuses are usually rated to interrupt at least 50kA, often 80kA or up to 200kA depending on size, etc., which might be useful if tapping power of a 3MW LV transformer...
So just to recap your information :
88-2 = industrial,
88-3 = domestic,
88-4 = fast fuses (motor drives, etc)
Tables in OSG
B1 (rewirable)
B2 (industrial)
B3 (industrial)
B4 (domestic)
B5 (domestic)
That is how I now understand it to be, with the B3/B4 being the one you would go to for any newer system or design work.