Discuss BS EN 60204-1 Help required re : Earth loop testing of machinery in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

M

markymark31

Hi Guys,

The 17th edition gives you a table of circuit breakers and their maximum allowed Zs, however as the 17th edition does not cover "machinery", we have just started working with BS EN 60204-1 "Safety of machinery - Electrical equipment of machines - Part 1 General requirements", and this standard does not have a similar table.

Annex A.2 does reference Zs / fault currents / voltages etc. but nothing that I can really get my head around.

Does anyone have any practical examples of how I can show my test readings and document the fact that these do (or don't) meet the requirements of this standard ?

Thank you,

Mark.
 
The Zs values for OCPD's are listed in BS7671, however they are not part of that standard. Your mcbs in your machines still have to comply, or else disconnection times will not be met. As for the appropriate times?
 
Thanks for the reply, disconnection times is the easy bit, these are stated in 60204-1. So is it the MCB standard itself that states the max Zs (60898 etc. ?) everywhere else I look it keeps referring me back to BS7671 ?
 

Reply to BS EN 60204-1 Help required re : Earth loop testing of machinery in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, I am an electrician working for a OEM machinery manufacturer based in Germany, we are the local hub that is now taking over the...
Replies
8
Views
988
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
Replies
2
Views
709
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Many will by now have heard of the new requirements for private landlords, enacted under Statutory Instrument 2020 No. 312, known as ‘The...
Replies
48
Views
13K
To keep your trainee brains in tip top condition during lockdown, here's a few quiz questions.... 1) A fault report is 'Circuit breaker keeps...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock