I recently came across an installation, very rough in practically all areas, however one thing caught my eye.

The TNS earthing arrangement was via a BS951 clamp onto the armour of the incoming supply cable. This wasn't a lead supply cable (as I have seen before with BS951 clamps) it was SWA with a section of the sheath cut and a clamp applied to the armour wires.

Now I am wondering if this is a DIY TNS as it is an old terraced house and a number of similar properties in the local area are TT earthing arrangement.

I am well aware that the incoming cable is the DNO property and if they see fit to supply an earth like this then so be it but it looks dog rough. What would your thoughts be?
20150618_123851_zpskz081deh.jpg
 
This is the thing it was a flying visit to do a recce on behalf of an estate agent. The tenant has made a complaint to the local building control/housing regulation regarding a number of issues and the building inspector cited electrical safety as one point.

I will ultimately be carrying out an EICR at the property but wanted some opinions on it before the time comes.
 
my first job would be a Ze to verify that the SWA armour was, in fact, earthed.
 
Does look rough. I think your best bet is to spend some time fully investigating it see what you come up with. Where is the CU?

CU (old wylex rewireable) is just to the right out of the picture. No main bonding whatsoever, only 2 circuits for whole of house (lights and sockets), big gaping hole in front of cover....

It's not looking good!
 
Listen to uncle Tel.:biggrin5:
 
I have no intention of doing anything other than listening to uncle Tel, I'm currently writing the estate agent a rather long winded email explaining why an EICR must be carried out without delay.

Do get rather sick of trying to explain to people (specifically tight a*sed landlords) why their installation is so unsafe while they try and tell me it has worked fine for years
 
my first job would be a Ze to verify that the SWA armour was, in fact, earthed.

If it is a row of properties,and the details of supply/earthing are not known,i would have a quick search of the route of your incomer/earth,BEFORE disconnecting,for your Ze. :yesnod:
 

Reply to BS951 clamp onto incoming supply SWA cable - DIY TNS? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
717
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
I have just completed an EICR. The earthing is TN-S. However, there is a BS951 clamp used for this. Is this acceptable? Did the DNO ever use this...
Replies
7
Views
3K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock