Installing a plastic board would not be to 17th Ed spec it would be compliant to the 18th Ed.
Failing to provide an earth wouldn't be to 18th edition spec either...your point is?
Did I mention a plastic board? I'm baffled as to why you have mentioned the plastic board?
 
Metal boards on a TT complicate things because of either the need to fit an up front S type RCD or take particular measures to prevent a fault to the case. Neither of these are issues with a plastic DB, and if a plastic board complies then it makes sense to use one. Cheaper, safer, not prone to corrosion.
A metal board makes no sense whatsoever.
 
But metal Db’s are now being fitted almost everywhere,you can still have a main switch ,then rcbos,with the tails supported by appropriate glands.
Metal Db’s rule...ok
 
Not again,a metal DB fine too....
Yes either metal or plastic is fine but additional precautions must be taken if you opt for metal. IMO in the Op’s Situation I would of used an IP rated plastic board like I linked to. I don’t understand really why you would want to introduce a potential that wouldn’t exist if a plastic board was installed...especially on a building site where things regularly get knocked/pulled about. Maybe the difference is actually understanding and going above and beyond the Bare minimum.
 

Reply to builders supply- amendment 3 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
848
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
So I need to add a new circuit, I was going to do it to amendment 2.. Its a commercial property and will be adding a new circuit for a...
Replies
22
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock