Here's a bit of guidance for anyone that has used the Klickfit (pull over tile and batton roof anchors) mounting system.

Once the local building authority knows you have used this system they will make you take it down at your expense!! as it goes against bre guidance and dti guidance and building control guidance (part A)

"you cannot fix a roof anchor to a batton in any way shape or form, you must fix to a rafter which is capable of taking estimated loads"

Spread 4 rows of rails across diffrent rafters to spread out load balance.

I think Klickfit have sold alot of this stuff in the UK and alot of companies thought it would save them time and money ooops!
 
@Bigbob1

Before you make a post like this please get your facts correct. In fact your post is actually potentially libellous.

Most people here know my background and qualifications, if you don't, then I suggest you do your research and dig through some of my posts BEFORE you respond.

1) I presume that you are actually referring to the ClickFit system.
2) If you are then it has been fully tested at BRE - I have a copy of the full and comprehensive test reports.
3) You need to understand how uplift pressures and dead load forces work on roofs, most of the Building Regs people don't.
4) The document referred to above has been well discussed on this forum and has already been changed due to pressure from folks here.
5) The document is guidance only from a non-authorative body.
 
I'm only relaying what Graham Evans Inspections Manager South has said to us and what Building Control for Essex County Council have said to us so no need to get your knickers all twisted up.
 
143 mph and all the click fit clamps bend totally out of shape, and the bottom corner comes off a panel, and that was just testing the up lift on the panels with clamps at 400mm centers!! with suckers attached that can't re-create the back and forth blow of the wind!! lets hope we don't have many big storms for your sake, luckily i can read that report and understand it. Maybe thats why in the guide's for all this they say you must not attach to a batton but the rafter that is geared up for load baring wieghts. Good job i have a guy with a 7 year carpentry and joinery apprentaship his hnd's and hnc's and advanced skills certificates in building roofs and he can say weather the roof will blow off!! beacause the click fit system will blow off if the roof isn't battoned properly. 2 panels where tested imagine if it was 16, 2 x 8 rows, 600mm rafters so there are 3m long battons all nailed once every 600mm??? thats not many nails!! JUST A CHEAP AND TACKY WAY TO SAVE £300 AND CUT DOWN ON 1 MINUTE A BRACKET!! Get Cleaner Air Solutions to do that rig in the BRE tunnel and see what happens when they stick it up to force 7 winds. Worcester you do whatever you want with your work mate but i will carry on doing it properly thank you.
 
Not getting my knickers in a twist, as you are obviusly knowledgable in this area, and with an experienced team.

Perhaps you would care to share what you do that ensures that you comply with Eurocode 5?

Appreciate your advice, so that we can all learn.
 
No Probs

Forget about Eurocode 5 untill you've looked at Eurocode 1 EN1994-1-4: 2005 http://www.thomastelford.com/books/...ide to EN1991-1-4 Eurocode 1 wind actions.pdf

Also look at this program it can help greatly WOODexpress - Design of Timber structures according to eurocode 5 this is Eurocode 5 software.

I have talked to alot of people about this as saving a bit of money on mounting systems is a no brainer but........

If you can imagine how easy it is to pull a nail with a hammer and you have roof anchors attached to a batton that can twist backwards slightly then you attach a wing to the anchors, when the right gust of wind occurs it will act like a hammer pulling the nail.
over a period of time constant moving on the anchors will loosen nails, so not 1 gust but repeated gusts can loosen and make that 1 gust take the batton off, on modern houses using a plas gun to put battons on can increase the risk even more as these nails somtimes go right into the batton. Particularly on properties in open areas surronded by fields for instance and the more you go above sea level.

It's just been expressed to me to avoid this mounting system like the plague, after looking into it i will.

Bob
 
@bigbob1 We all have our feelings on this, so I'll respect yours on this.

So that stillleaves the question: How are you / what are you doing to comply with Eurocode 5 Table 8.6?
This is a major problem on 35 mm trusses.

What's your magic answer?

I'd appreciate your help on it.
 
hi!!

My magic answer is........... fixing to the top of a rafter has nothing to do with axially loaded screws!! so table 8.6 of eurocode 5 has absolutely nothing to do with mounting a roof anchor!!. As your not loading the screw in tension, or creating a shear force on a structural joint.

Don't just take my word for it as i'm sure you won't. Phone up a chartered structural engineer like i have!

If you where placing the roof anchor inside the roof underneath the rafter then this would be axiall loading!

Once the engineer has e-mailed me the information you will need, i'll link it here.

Untill then you have a really good weekend proffessor.
 
If you where placing the roof anchor inside the roof underneath the rafter then this would be axiall loading!

Once the engineer has e-mailed me the information you will need, i'll link it here.

Thanks BigBob1, I'd really like to see that email.
 
What you have linked there is what was said on the phone.
this is the information he sent me >>Refer to BS 5268 part 2:2002 Appendix G for your screw type's and lengths.

and this is the email he sent saying the thickness of an acceptable screw>> to be put in to a pre drilled hole.

Hi Robert.

As long as the diameter doesn’texceed (3.8mm) say 4mm that will be fine.

Chris

Ken RushAssociates
Bowman House
191 South Street
Braintree
Essex
CM7 3QB
tel: 01376 326789
fax: 01376 342711
Technical email: [email protected]
Adminemail: [email protected]


for fitting to the top of a 38mm rafter as everyone i've spoken to says it's 38mm not 35mm, no more than shaft thickness of 4mm for the screw. So 3mm pilot hole 4mm screw shaft.

Hope this resolves issue, contact him if you want he's a nice guy, and will explain axiall loading to you if you really want to know, as i think you where a bit confused as to what it was/is.
 


Hope this resolves issue, contact him if you want he's a nice guy, and will explain axiall loading to you if you really want to know, as i think you where a bit confused as to what it was/is.

I think you'll find you've underestimated Worcester, I suggest you review his posts :)
 
That's the exact problem Bigbob!, can you show us a picture of one that you've fitted with 4mm screws then please.
 
SRE he wouldn't be on here if he had done 7 years at college to become a structural engineer would he?

I suggest you check out SIG fixings, you can get a 4mm shafted hex head zinc coated wood screw.

cheers
 
i'll take a load of pictures for you to show you how to fix an anchor with a 4mm bolt to a rafter not a problem.

I suggest you use a person that is competent at being able to evaluate a structure and give you proffesional advice on how to go about doing your work on that structure. It seems you don't.

I can't see what the problem is with finding the correct fixing to do the job i don't struggle with that??

If a chartered structural engineer, that you can contact and talk to about this (please do!) says that a 4mm screw is okay for a 38mm rafter then what is the problem??

I think your just a bit annoyed that you've been pulled for even thinking about using the crap clickfit system and are obviously trying to move away from that fact, by quoting stuff from charts (EC5 table 8.6) that has absolutely nothing to do with this etc etc axially loaded screws etc etc.

I have never claimed to know everything about this but some people appear to think they do. I have not got a problem asking the right people the right questions to get the correct answer.

So it brings me to this, "How do you fix to a 38mm rafter???" OH YEAH you use clickfit!!!!

Some people eh!!
 
SRE he wouldn't be on here if he had done 7 years at college to become a structural engineer would he?

I suggest you check out SIG fixings, you can get a 4mm shafted hex head zinc coated wood screw.

cheers


I'm not sure I get your point about going to college for 7 years meaning he shouldn't be here??? I've been to college for a similar length of time does that mean I shouldn't be here either? I'm not keen on Clickfit but don't feel the need to critical of either perspectives, it's a personal choice that you each have to be happy in your own mind is suitable for your installs. No need to attempt to bludgeon anyone into submission with superior knowledge or be disrespectful of other points of view.

I'm guessing that it's been a long week for everyone :)
 
I'll take a load of pictures for you to show you how to fix an anchor with a 4mm bolt to a rafter not a problem.

Many thanks Bigbob1 would really appreciate that, it's always good to learn from experienced people, - What anchor / fixing system are you using with those screws?
 
Schletter mounting system

You'll have to talk to SIG fixings and ask them to get hold of those bolts, i just get 500 a time bout £25. They do a sealing washer as well that will fill any gap up in the roof anchor hole when a washer comes down on top so there is no movement in the bracket once fixed, and these are designed for roofing applications so have a long life and don't perish. they do a fixing that you use a ratchet on and also one that can be done up with a battery drill.

They also do a self drilling fixing for wood application but i think this is a no no.

One i'm starting on the 5th September has 38mm rafters.
 
Schletter mounting system
One i'm starting on the 5th September has 38mm rafters.

Would be great to see the photo's on that, thanks
 

Reply to Building Control Guidance on Retro-fitting Solar Panels in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Can someone recommend an immersion controller that turns the immersion on when the is excess power from solar panels. Thanks
Replies
2
Views
487
My best mate has been medically retired from the prison service at the young age of 52 and has time on his hands :D He's looking at a 'plug in'...
Replies
7
Views
414
Hi, So I'm replacing a small old off grid with a new 7.5kw off grid, & being poor seek best value for my mppt, after long searches I find this...
Replies
1
Views
619
Hi all I'm looking for some help on a query I have. I'm currently involved with a new build with the plan to fit Solar in the very near future...
Replies
1
Views
913
Hi, I plan to add solar to my home and have a question about how many amps I can backfeed into my AC service panel using Net Metering. I know NEC...
Replies
1
Views
814

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock