Hi all
can someone please tell me is it in the regs that capping must be used when burying t&e cables in a plastered wall.
Thanks
 
Don't think its a must, more a personal choice.

All capping does is protect the cables from damage until, or whilst being plastered.

It can make rewiring at a later date easier, as cables can just be drawn in.
 
Last edited:
Hi, just found this on the net, maybe of some help or maybe no help at all.

Regulation 522-06-06
A cable concealed in a wall or partition at a depth of less than
50 mm from the surfaces of the wall or partition shall:
(i) incorporate an earthed metallic covering which complies with
the requirements of these Regulations for a protective
conductor of the circuit concerned
, the cable complying with
BS 5467, BS 6346, BS 6724, BS 7846, BS EN 60702-1 or
BS 8436, or
(ii) be of insulated concentric construction complying with
BS 4553-1, BS 4553-2, or BS 4553-3, or
(iii) be enclosed in earthed conduit, trunking or ducting satisfying
the requirements of these Regulations for a protective
conductor
, or be mechanically protected sufficient to prevent
penetration of the cable by nails, screws and the like
, or
(iv) be installed in a zone within 150 mm from the top of the
wall or partition or within 150 mm of an angle formed by two
adjoining walls or partitions. Where the cable is connected to
a point, accessory or switchgear on any surface of the wall or
partition, the cable may be installed in a zone either
horizontally or vertically, to the point, accessory or switchgear.
Where the location of the accessory, point or switchgear can
be determined from the reverse side, a zone formed on one
side of a wall of 100 mm thickness or less or partition of
100 mm thickness or less extends to the reverse side.

So basically if the cable is not in one of the acceptable zones and it is not more than 50mm deep, it needs protection, and capping does not provide protection.
 
There is no need or regulation requiring protection of T+E installed in correct areas.

My last rewire all went in oval conduit to protect from trowel damage by plasterers.(Personal preferance)

Did cost me about a tenner more on materials but at least I wont have to f*** about trying to replace damaged cables at a later date.

CBW
 
REG 522.8.1. A wiring system shall be selected and erected to avoid during installation, use or maintenance, damage to the sheath or insulation of cables and their terminations.


Now to me, that means use capping/tube unless its a new build and the walls are either i) stud walls or ii) dot and dab (I still put it in tube)

I for one, use oval tube every time, it looks more professional than clipping straight to the wall, its easy enough to do, gives it a bit of protection when other trades are working on the same building, and if you are ever called back to a burnt out socket, you have a fighting chance of pulling some slack down to do a repair.
 
Last edited by a moderator:
So basically if the cable is not in one of the acceptable zones and it is not more than 50mm deep, it needs protection, and capping does not provide protection.


'needs protection' doesnt mean by capping alone. it means protection by an rcd. so you can put cables into plaster direct , if protected by an rcd, its just not good practice. also even if cables are run in prescibed zones they still need protection by rcd unless run in earthed metal conduit or deeper than 50mm.
 
As I understand it, if you do not protect the cable from the plaster then over time the cable will become brittle. I've been told the some of the materials, possible lime, in the plaster will eat away at the sheathing causing it to become brittle and then break down the insulation over time.
This might take years but always better to be safe than sorry!!

Hope this helps.

Dave
 
As I understand it, if you do not protect the cable from the plaster then over time the cable will become brittle. I've been told the some of the materials, possible lime, in the plaster will eat away at the sheathing causing it to become brittle and then break down the insulation over time.
This might take years but always better to be safe than sorry!!

Hope this helps.

Dave

This is an urban myth; Plaster does not chemically attack PVC. Nor does cement, but due to the heat generated in the curing process; it is prudent to try & counteract this if possible.
 
Hi, just found this on the net, maybe of some help or maybe no help at all.

Regulation 522-06-06
A cable concealed in a wall or partition at a depth of less than
50 mm from the surfaces of the wall or partition shall:
(i) incorporate an earthed metallic covering which complies with
the requirements of these Regulations for a protective
conductor of the circuit concerned
, the cable complying with
BS 5467, BS 6346, BS 6724, BS 7846, BS EN 60702-1 or
BS 8436, or
(ii) be of insulated concentric construction complying with
BS 4553-1, BS 4553-2, or BS 4553-3, or
(iii) be enclosed in earthed conduit, trunking or ducting satisfying
the requirements of these Regulations for a protective
conductor
, or be mechanically protected sufficient to prevent
penetration of the cable by nails, screws and the like
, or
(iv) be installed in a zone within 150 mm from the top of the
wall or partition or within 150 mm of an angle formed by two
adjoining walls or partitions. Where the cable is connected to
a point, accessory or switchgear on any surface of the wall or
partition, the cable may be installed in a zone either
horizontally or vertically, to the point, accessory or switchgear.
Where the location of the accessory, point or switchgear can
be determined from the reverse side, a zone formed on one
side of a wall of 100 mm thickness or less or partition of
100 mm thickness or less extends to the reverse side.

So basically if the cable is not in one of the acceptable zones and it is not more than 50mm deep, it needs protection, and capping does not provide protection.


Isn't this reg all about 'additional protection' ? Basically saying that if it doesn't meet all of the above then it needs additional protection of a 30mA RCD.
 

Reply to burried cables in the Australia area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
601
Hi everyone, I intend to bury a 240 volt cable from my house to my barn about 7 metres as way. It will be buried under my tarmaced drive which I...
Replies
7
Views
316
Hi, I have two questions about domestic wiring In Ireland 1. Should conduit be used when passing multiple T&E cables (2.5mm) through a garage...
Replies
6
Views
770
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
649
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
502

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock