:cool:jus finished 4 xmas,last job was to add extra 2g sockets in school,these were supplied off local circuits.Doin the test procedures,even wiv our non trip ELI meter the rcd tripped,so i attempted to by pass rcd & then test.We all no this isnt the easiest thing 2 do,the rcd gave a little bang & tripped,reset & tried again,exactly the same thing happened,now doin it twice was fine but theres no way a third time,reset & ok.Any1 --- across this the, rcd is a BS4293,63 amp 30ma mayb 15 -20 years old MK.So.. no test were performed on circuit,this was noted,but u can jus imagine when new term starts,it was ok untill u lot came,hav a gud 1 ta ra bab:cool:
 
so, ramp test the rcd. if faulty replace the dasmn thing. job done
 
Ramp test the RCD, never bypass it. The Zs test measured will require the RCD in circuit for an accurate reading.
If the ramp test doesn't confirm a faulty RCD, try your low trip on another RCD to verify that the tester is putting out a low enough current under test. If the low trip works fine, then go back to thinking about changing the nuisance RCD.
 
if you were to bypass the RCD you would be leaving the installation in a more unsafe condition. make sure you leave a MR. Electric invoice and job sheet.
 
yeah the by pass was only 2 test the zs on circuit,both testers on the low settin were takin rcd out,bit of a ball ache 2 change db,mk 8 way ,rcd up front,will need rcbos etc,all because we added skts,a PIT sticker on db shows tested last year. A new year job already,thanks all merry xmas & new year.
 
If you need in future to test for Zs and have a no trip meter or even a soft trip that trips the RCd then you could do:

Isolate the circuit from the MCB and lock off. Link phase and earth out at the end of the circuit. Then at the DB one probe on the load side of the MCB you have isolated and the other probe onto the main switch or supply side of the RCD, do your EFLI test and that will be the ZS for the circuit. Then AFTER DISCONNECTING THE LINK reset MCB

Merry CHristmas.
 
:cool:jus finished 4 xmas,last job was to add extra 2g sockets in school,these were supplied off local circuits.Doin the test procedures,even wiv our non trip ELI meter the rcd tripped,so i attempted to by pass rcd & then test.We all no this isnt the easiest thing 2 do,the rcd gave a little bang & tripped,reset & tried again,exactly the same thing happened,now doin it twice was fine but theres no way a third time,reset & ok.Any1 --- across this the, rcd is a BS4293,63 amp 30ma mayb 15 -20 years old MK.So.. no test were performed on circuit,this was noted,but u can jus imagine when new term starts,it was ok untill u lot came,hav a gud 1 ta ra bab:cool:

Is this some kind of Foreign language ?? :)
 
Golden boy
Not up to youngspeak standard I'm sorry,you will have to practice more
Your words did sound to me like the black folk in "Gone with the wind" though :)

OMG PMSL, BTW don't be dissin da yun uns innit. Goin bak 2 ma crib in me 400bhp punto 2 whatch Ali G. Heees baad. C yas, piece out 4 now, layters.;););)
 
.make sure you leave a MR. Electric invoice and job sheet

Excuse my ignorance but have seen this type of comment a few times on this site and was just wondering what the deal is with them.

Being from the distant corner of the UK there is no MR Electric on our shores. Had a wee look on the net and it appears they are a national company. Take it they are famous for their incompetance and dodgy work at high prices?
 
They are primary associated with insurance companies that offer the call out cover on a policy. In all fairness they are an American Franchise and a lot of their practices are to say the least cheesy. You turn up in your shirt and tie and put down a outside carpet so you can wipe your feet and even supply their guys shoe covers and such.

What the trouble is they tend to get called out and in all fairness they do tend to find and repair the fault, but they then try and drum up business by highlighting to a non technical person that their installation is not up to the latest standards and the bonding is not right and there is a lack of RCD protection which the new standards recommend, so though technically they are correct they omit to tell the person that the installation is still safe and even if you didn't spend hundreds upgrading to the 17th, you would not be in any mortal danger.

so they tend to get frowned upon as much do the British Gas service.
 

Reply to Bypassin rcd in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
768
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
1K
Had a real headache of a fault finding job which has left me scratching my head - RCCB on a split load board, supplying 3 circuits (shower...
Replies
20
Views
4K
Hi, an Electrician recently replaced all switches, sockets and spot lights. They also appear to have connected an RCD to the fusebox or installed...
Replies
16
Views
21K
Doing standard tests prior to some minor works on a socket circuit (Zs, IR etc), pressed the test button on the RCD, tripped fine, got ready to...
Replies
3
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock