stretchyboy

-
Arms
Reaction score
8
I have quoted for a job of fitting a CT chamber and doing the intake alterations to change a 100A 3-ph supply to 200A 3-ph and in doing so obtained a price for the CT Chamber from Ryefield. The metering company need to know the CT ratio to complete their form so they can book the job, so the client asked me for this info. I got on to Ryefield who said that they dont supply the CT coils ??? and as far as I remember from last time I installed one they came in the chamber already, so now i'm trying to get an answer while Ryefield have finished for the week at 2PM and no-where on-line can I find a decent pdf of the kit to look at ................. help :eek:
 
As far as i recall a standad meter kw/h requires a a current between 0 to 5A so if you had a 200amp supply i believe you need a ratio of 200/5, the 200 is proportional to your current you are measuring and the 5 is a standard secondary current for the meter.

Thus a 100amp supply would need c.t.s with a 100/5 ratio etc

I think this is how it works when choosing your c.t.s but be best to look up some c.t.s in a catalogue and ring tech for advice which is only the cost of a phonecall, they are always happy to help and this is how i learn alot of things college never taught me.

Note you will probably have to price for a c.t. per phase
 
Last edited:
cheers, that helps, but Ryefield are an old firm that finishes early on a friday and I seem to remember ringing 'during their lunch hour' once too ;-( so their technical probably wont be around until Monday midday after tiffin and jam sandwiches. :D
 
I installed a 600A Ryefield ct chamber a little while back, CT's were supplied by the metering co.
Scottish & Southern I believe.
 
Please be aware you need to specify metering CTs as these are different from protection CTS , also the supply authority will require a certain class of CT ( 0.5M) ( 0.1M) etc
 
Please be aware you need to specify metering CTs as these are different from protection CTS , also the supply authority will require a certain class of CT ( 0.5M) ( 0.1M) etc
I do hope he's sorted this out by now as its nearly 4 yrs old since this thread was posted but you could be lucky as he might still be waiting in a queue for technical support......... You are no3 in the queue ....we will be with you shortly!
 

Reply to C T Ratio in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock