Cable calcs using cable calc app
Working out cable size for a workshop.
100m long, 100a supply, mccb 100a zs- 0.23 ohms, in a duct on its own, tt earth on 300ma rcd.- 20 ohms

App says 50mm swa which I expect.

But if I alter earthing to tncs 0.35 ohms it says max ze exceeded zs of device.

Am I missing something here / Friday afternoon brain.

Thanks
 

Pretty Mouth

-
Esteemed
Arms
Reaction score
2,341
For TT, the app is using the RCD for protection against earth faults, as you would - the OCPD almost certainly would not operate for fault currents on a TT system.

When changed to TN-C-S, it appears the app has decided to use the OCPD for protection against earth faults. However you can use an RCD for this protection on TN systems, it's perfectly acceptable (all other things being correct)
 
OP
Simon-0116
Reaction score
22
For TT, the app is using the RCD for protection against earth faults, as you would - the OCPD almost certainly would not operate for fault currents on a TT system.

When changed to TN-C-S, it appears the app has decided to use the OCPD for protection against earth faults. However you can use an RCD for this protection on TN systems, it's perfectly acceptable (all other things being correct)
Thanks
Always wondered what people do when device operating zs is lower than ze. Never practically come across it till now.
 

Reply to Cable calcs zs and ze values in the Industrial Electrician Talk area at ElectriciansForums.net

Similar Threads

I am looking at a scenario of temperature compensation in a text book (Practical Guide to Inspection, Testing and Certification of Electrical...
Replies
6
Views
2K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
3K
Hi, first question on here in a very long time, I am hoping for some nice replies ?. It's been playing on my mind all week and can't seem to find...
Replies
12
Views
2K
Hi chaps. On some remedial works at a school, I have a sub main a 16mm armoured feeding it about 50m away from the main DB. Fed from a C63...
Replies
39
Views
10K
Can anyone help me understand Zs values. In the On-Site-Guide page 60 Table 7.1 under the heading Maximum cable length, it states if Zs < 0.35...
Replies
27
Views
8K

New Posts (Please Reply)

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top